Thread: Service Manual of Midea Chiller
07-06-2013, 05:33 PM #1
Hi..friends
i need service manual for Midea chiller and below is the model number of it:
MGB-F65W/RN1
thanks in advance.
07-06-2013, 08:42 PM #2
Re: Service Manual of Midea Chiller
08-06-2013, 05:48 PM #3
@install monkey: many thanks for the info.. still i want to know that, is it possible if i make the chiller continuously running on cooling mood or is it possible to reduce the time up to 2 minutes after the completion of chilled.
08-06-2013, 05:59 PM #4
maybe reduce the differential but typically u want 2 deg, also u still need a delay between starts- usually 3 mins, if you start compressors too frequently youll increase your electric bill and damage contactors,compressors- u might be able to lower ur setpoint but then u increase the risk of tripping on frost protection, maybe adding glycol (antifreeze) will allow a lower running temperature, dont know if theres an option to do this