Results 1 to 11 of 11
    3,357
    Frick oil injection
    After some opinions on a Frick with differential oil pressure feed system. Nh3 -10 sst +35sct, water cooled oil cooler. If oil injection regulating valve feeding into rotors is open to far, what medium to long term result would you get apart from lower than normal discharge temp. Thanks
    3,357
    Re: Frick oil injection
    I will also add that it runs on a VSD down to 25hz.
    Jun 2011
    Australia
    44
    336
    21
    Sounds like you know more than you are saying here. With conditions described, at low speed it's probably pumping more oil than refrigerant, an energy penalty at least. Long term could lead to bearing failure, I know of instances where oil compression was causing the compressor to make a hell of a noise with all sorts of internal stresses due to too much oil injection.
    Auckland
    74
    3,357
    37
    Hi Ranger1 I have a small Frick screw, similar operating conditions and VSD, it has wear in capacity slide. Modified control to keep fully loaded on capacity slide and VSD does capacity control, seems to have stopped any further wear after last strip down and inspection. I have kept minimum hertz to 35. max at 60. I had overcurrent issues with lower than 35Hz and capacity slide at 100%.
    3,357
    Quote Originally Posted by HVACRsaurus View Post
    I am only trying to confirm what I am thinking, no secrets or anything. What I do know is screw failed with approx. 30 000 hours on it. Oil injection open all the way thinking it may have caused oil compression under all loads! Male thrust failed toward suction end eventually causing seizure.
    3,357
    This ones a bit bigger 233 Frick, wasn't sure if orifice in oil injection was enough to control oil flow into rotors, but Danfoss 25 mm regulating valve fully open on inspection. There was no hint of potential seizure, it just seized while running.
    Auckland
    74
    3,357
    37
    Hi Ranger 1.ouch!! that is a large compressor to crash. Some one playing with danfoss reg valve. not understanding implications of over injection. The thrusts would have lost tolerance with extra loading.
    3,357
    Quote Originally Posted by abrahamlinkon View Post
    Is this process really working? because i also do this process and the result is nothing good.
    Can you tell me again how you did this...?
    Can you elaborate on your question, as not sure what you are referring too.
    May 2009
    New Zealand
    141
    15
    The orifice built into the compressor oil injection port is sized for max amount of oil at given FRICK design conditions. Is the orifice in place? Does the compressor run unloaded at 25hz? As said above, the pumped oil to gas ratio would be excessive I would think. I would be contacting FRICK to see if the comp is running within design. Could perhaps have oil injection thermstaticly controled?
    Sep 2008
    Canada
    811
    You can compare discharge temperature and oil inlet temperature. Usually, it is 50-60F difference. If this difference significantly lower than these numbers, probably too much oil going in.
    3,357
    Coolware has a standard 82C discharge temp for everything in their selection software. Oil injection orifice is in with oil injection regulating valve throttled. JCI put it in with a motor that to small as well. Compressor limited to 28hz & would have to check if it unloads at this minimum speed. Any idea what Frick do with oil injection? Do they turn it on/off on discharge temp or speed?