    On coil / off coil temperature
    hi all i am new to HVAC . i just want to how to find out on / off coil temperature.
    for example : Outdoor temp 45 deg and 90 RH
    Room temp 24 deg and 50 RH
    MY AIRFLOW IS 16250 CMH
    SENSIBLE LOAD 54.85 KW
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Apr 2008
    u.a.e
    43
    417
    Re: On coil / off coil temperature
    Quote Originally Posted by GIRI View Post
    on coil of AHU/FCU= air entering temperature
    off coil of AHU/FCU= air leaving temperature
    Jun 2013
    SINGAPROE
    4
    Quote Originally Posted by moideen View Post
    Thank you moideen,
    I just want to know how you will finalise the on coil and off coil temperature. is there any regulation or formula..?
    May 2012
    54
    1,325
    30
    Rough rule of thumb is 10 degs difference.
    Air off is lower than air on and if it is 10 degs lower then
    the thing is working.
    (this is a rough rule of thumb that is a guide only)
    Rob
    Feb 2007
    2,477
    First you would have to determine what type of kit you are looking at.
    In your example above, for the indoor coil, the on coil temp would be 24 degrees for a recirculating unit and 45 degrees for a 100% fresh air unit...
    The off coil temp should then ideally be around 10 degrees below your room temp i.e. 14 degrees (assuming we are talking cooling and not heating...).
    Jun 2013
    SINGAPROE
    4
    Quote Originally Posted by The Viking View Post
    thank you all for your information
    Mar 2010
    Vietnam
    33
    Fresh AIr Ratio? Supply air flow?