    Elitech STC9200 parameters



    As more rubbish is allowed into Australia from China I have found a controller on a job that I cannot find the parameters on the www ( everyone wants to sell them not actually set them up )
    so if you have the parameters or know the url location for this particular controller let me know.

    I found some once but they didnt match , when I press set + Down arrows I get F1 & F2 which look like setpoint and differential , thats all ?




    60% of the time it works everytime.

  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Elitech STC9200 parameters

    Hi Toolman.
    Not a lot out there is there!
    I found a little with reference to settings.
    Follow the link.
    Grizzly

    http://huaqiang909.en.made-in-china....STC-9200-.html

  3. #3
    Join Date
    Jan 2006
    Location
    Adelaide , Australia
    Posts
    192
    Rep Power
    19

    Re: Elitech STC9200 parameters

    Thanks Grizzly , it was a while ago I looked at that control and I think it had a lot of "F" parameters which make no sense at all !! The parameters in your link ( below ) makes sense .... so I have said if I have to do anything to these cabinets , I will just fit a Carel Or Dixell in place of the Piece 'O' Crap.

    menu
    us SET-50º C +20 Max. temp. sev. value
    ls -50º C-SET -20º C Min. temp. set value
    ac 0-50min 3 Compressor delay protection
    idf 0-120hours 6 Defrost cycle
    mdf 0-255min 30 Defrost time
    dte -50º C-50º C 10º C Defrost termination temp.
    fdt 0-100min 2 Wter-dripping time after defrost
    tdf 0: Electric-heating defrost 1: Thermal defrost 0 Defrost mode
    dct 0: the interval of defrosting actually 1: the accumulated time of compressor operation 0 Count mode of defrost cycle
    dfd 0: normal temp. display 1: defrost start-up temp. 0 Display mode when defrost
    fnc 0: under control 1: continuous operation, OFF when defrost 2: start/stop with compressor, OFF when defrost 0 Fan operation mode
    fot -50-defrost upper limit temp. -10 Fan start-up temp.
    fod 0s-255s 60s Fan start-up delay
    fst Fan start temperature-50º C -5º C Fan stop temp.
    alu ALL-50º C 50º C Alarm value when exceed upper limit
    all -50º C-ALU -50º C Alarm value when exceed lower limit
    ald 0-99min 15min Temp. alarm delay
    ot -10º C-10º C 0º C Temp. calibration
    Last edited by Toolman; 01-08-2013 at 10:04 AM.