    Exclamation Hitachi DC Inveter Scroll Compressor Start up Problem



    a 5.1 KW Hitachi DC Inverter Scroll Compressor have a startup problem. when i start the unit the compressor start a voice of " Tak, Tak , Tak rasie and after 30 Second the compressor trip, after few minutes the compressor again try to start and again Tak, Tak, raise and compressor trip. please somebody help me about this issue.

    Kind Regards
    M.Arshad



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Hitachi DC Inveter Scroll Compressor Start up Problem

    test output voltage from inverter, accross terminals, should be the same, either inverter pcb or compressor goosed, but then has something else caused this, if replacing the compressor then replace the inverter kit too

  3. #3
    Join Date
    May 2013
    Location
    Pakistan
    Age
    35
    Posts
    5
    Rep Power
    0

    Re: Hitachi DC Inveter Scroll Compressor Start up Problem

    Thanks for your reply.

    I want to ask from you the compressor fault occur due to the inverter PCB ? or it's mechanical fault?
    PCB is ok I have check the PCB.