proove ur getting 3 phase to the contactors, if your not then a fuse,contactor issue, if you are clip the current to see if ur pulling around 160amp,then compressor siezed
-
27-05-2013, 07:24 PM #3
Re: any suggestion about this problem ..
I did all the recommended steps ...especially the 3 phase connection but the ( 9 ) compressors was sized...
-
27-05-2013, 07:55 PM #4
Re: any suggestion about this problem ..
inspection cover on them is underneath,so theyre a bugger to inspect,cheapest option is to get them refurbished and replace all contactors,overloads,fuses
-
27-05-2013, 08:55 PM #5
Re: any suggestion about this problem ..
Hi take the oil pump off and by using a large flat screw driver spin the crankshaft and see how it feels. If tight or siezed youll be able to tell it
-
27-05-2013, 09:05 PM #6
Re: any suggestion about this problem ..
They are 33 (!) years old...
If you are to use them your best bet is to get them overhauled by a professional compressor refurbishment outfit that would strip them and give them new bearings/seals/windings.
But really? What would you do with a 30 year old car that didn't start???
-
29-05-2013, 05:29 PM #7
-
29-05-2013, 06:58 PM #8
Re: any suggestion about this problem ..
Also these comps have robert shaw motor protectors and control modules. So kriwan int69 module wont work. And fsm modle is a 50% part wind start