    a condensor freeze



    we have a glycol chiller, ethylin glycol temperature about -15dc,the chiller is insde a plant room.
    this spring ,the condensor were sondenly discovred freezed,with more than 10 tubes broken. this phonemonen has never encourtered before, who know the cause please?



  2. #2
    Join Date
    Jan 2008
    Location
    north west
    Age
    42
    Posts
    234
    Rep Power
    19

    Re: a condensor freeze

    If its frozen up I would assume your glycol levels are incorrect.

  3. #3
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: a condensor freeze

    To get to the root of your problem your best option is to get an experienced refrigeration engineer in to look at your chiller.

    Sadly my psychic powers does not stretch for thousands of miles and what can be achieved over the internet is somewhat limited, sorry.


  4. #4
    Join Date
    Jul 2013
    Location
    Hampshire
    Age
    40
    Posts
    6
    Rep Power
    0

    Re: a condensor freeze

    I'd have to agree with 1mikeefc1's that the levels are probably incorrect. If you're wanting to do some reading up on Chiller Glycol I found this short article useful

    http://www.icschillerservice.co.uk/g...iller/07/2013/

    They've given me advice in the past about different different types of Glycol.

    Mono Ethylene, a general food & beverage grade antifreeze.
    Mono Propylene and FlowCool Green this is a food safe biodegradable antifreeze made from a proprietary blend of refined vegetable extracts that are biodegradable and have a very low order of toxicity. Suitable for use in the food and beverage industry or for systems where low oral toxicity is preferred. It's non-toxic (GRAS) multi-metal inhibitors helps protect chillers and associated cooling systems against corrosion and scale, thus prolonging equipment life and thermal efficiency.

    Hope you find that information useful, welcome to the world of Glycol

  5. #5
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: a condensor freeze

    Quote Originally Posted by wangxiaomin View Post
    we have a glycol chiller, ethylin glycol temperature about -15dc,the chiller is insde a plant room.
    this spring ,the condensor were sondenly discovred freezed,with more than 10 tubes broken. this phonemonen has never encourtered before, who know the cause please?
    This phenomenon can heppend when you call the evaporator, condenser......
    The cause is [ like my destinguished Colleagues said] wrong % of glycol or chiller running when circulation pump is still.
    When was the last time anyone have checked it?

  6. #6
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: a condensor freeze

    Water cooled condenser frozen while shut down, had similar problems in Siberia. the water was not drained from condenser during shut down winter period as instructed. Very messy and expensive repair and clean up of system.

  7. #7
    Join Date
    Nov 2013
    Location
    Canada
    Posts
    10
    Rep Power
    0

    Re: a condensor freeze

    Check the power supply mode is it normal or not ? Set the power supply in normal mode with using stabilizer.If refrigerator condenser is not working properly then replace it.