    Aug 2009
    utah
    83
    9
    Internal Pressure Relief
    What symptoms will occur if the (IPR) is parttially open? Would I have lower than other than normal suction and superheat at the evap .
    Aug 2009
    utah
    83
    9
    Re: Internal Pressure Relief
    Would I have higher current draw as well
    Oct 2003
    56
    5,519
    28
    HP and LP will be almost the same, compressor body will be extremely hot and AMPs will be lower.
    Jan 2007
    India
    13
    At the time of IPRV opening , you can hear the audible noise. The suction and discharge pressure equalizes rapidly
    Regards,
    Sendhil