    Air/ moisture in system ?



    On a 404A system...taking the receiver tank temperature and pressure....using the pressure / temperature chart.............I am showing 2 lbs psi more than what the chart calls for........ my question is....... is this with in range ? Would that cause high head pressure ?



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Air/ moisture in system ?

    Is the system operating or standing still?
    How accurate and calibrated are your gauge and thermometer?
    How confident are you in your readings?

    2 psi out, that is less than a degree... No field instrument will have that sort of accuracy and even if it did just a layer of paint or a slightly tilted probe would throw it out by more than a degree.

  3. #3
    Join Date
    Jun 2010
    Location
    USA
    Posts
    89
    Rep Power
    14

    Re: Air/ moisture in system ?

    I used 2 different sets of gauges and temp probes....the unit was off for about 3 hours ...so do you think its save to say the system does not have air in it ?

  4. #4
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Air/ moisture in system ?

    You are better off observing the pressure - temp relationship whilst the system is operating.


  5. #5
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    51
    Posts
    1,083
    Rep Power
    23

    Re: Air/ moisture in system ?

    Yes it is safe to say system has no non-condensables in it. Dirty/dusty condenser, airflow or high load could cause high head pressures. If it troubles you post the system parameters and we will help.