Results 1 to 16 of 16
15-05-2013, 10:19 AM #1
starting gear of mtz32jf5ave compressor
Hi was wondering if someone could tell me if this is wrong as the starting capacitor is over heating and burning out after 5mins. Its for a danfoss mtz32jf5ave compressor thanks much appreciated if someone could help me out
15-05-2013, 12:02 PM #2
Re: starting gear of mtz32jf5ave compressor
The bottom 1 is the wiring diagram thanks
15-05-2013, 12:04 PM #3
The bottom diagram is the wiring im trying to replicate thanks
15-05-2013, 03:52 PM #4
You appear to have the start winding in constant,normally on relays live into no5 and linked from there through klixon to common,neutral through start capacitor to contact 1,neutral through run capacitor to contact 2,neutral direct to R run winding,connect contact 2 direct to S start winding.The start capacitor is in series with the start winding only when motor is starting,when the relay drops out so does the start winding . The run capacitor is in parallel with the start and run windings.
16-05-2013, 11:57 AM #5
Like this ??? Thanks for the reply
17-05-2013, 12:37 PM #6
This is what danfoss tech help have told me but its blowing trip as soon as compressor starts
17-05-2013, 12:40 PM #7
This is how climate tech told me how to wire it, it is also blowing trip as compressor starts. You really appreciate if someone could point me in right direction thanks
17-05-2013, 12:41 PM #8
17-05-2013, 01:05 PM #9
Most compressors ive worked on send the phase direct to the common and neutral through relay ,probably make no difference the other way around.Your problem is if you ran the compressor according to your first diagram you more than likely have burnt out your start winding,Meggaring the windings will confirm if this is the case
17-05-2013, 03:07 PM #10
After I tried the wiring from danfoss an climate I wired it back the way it was an the compressor ran. It wasnt me that wired it there was some1 at it before me. If I meter the windings an find them ok would you have any suggestions as to what it could be ? Thanks
17-05-2013, 03:47 PM #11
Any chance of a photo of the relay front connections and model numbers
17-05-2013, 03:58 PM #12
No problem ill get a pic this evening thanks for your help
17-05-2013, 04:25 PM #13
Front of relay
17-05-2013, 04:28 PM #14
Numbers on relay
17-05-2013, 07:47 PM #15
The first drawing has the start winding wired as the run winding with a permanent live, and the run winding wired as the start winding with the capacitors connected across it. I expect that there wasn't enough voltage from the run winding to cause the relay to drop the start cap out of circuit which is why it kept over heating. I would not be surprised is damage has not been done to the motor.
What are the correct resistances for the windings, and do yours match up?Mostly found in Oxfordshire, UK :)
17-05-2013, 08:24 PM #16
I give the resistances of windings to danfoss and they told me they were ok