    Crankcase heater wired in series with compressor



    Recently I came across a Bryant heat pump with a 1.5-pole contactor. They had the crankcase heater wired up across the side of the contactor that breaks the circuit, i.e. one side of the heater connected to L1 and the other side connected to T1. This was consistent with the wiring diagram.

    When the contactor is pulled in, there will be no potential difference between L1 and T1, so the heater won't do anything.

    Here's where it seems funky to me. When the contactor is not pulled in, the crankcase heater is essentially wired in series with the compressor windings. Apparently the voltage drop through the heater is high enough that the compressor won't spin; instead, the windings will heat up (and help keep the crankcase warm).

    Am I understanding this correctly? It seems like that would be hard on the windings. And what happens if the crankcase heater partially shorts to ground?



  2. #2
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    51
    Posts
    1,083
    Rep Power
    23

    Re: Crankcase heater wired in series with compressor

    Hi Jeremy
    It would seam probable that you have miss interpreted - all good the contact energises and compressor comes in and cch drops out, on de - energise the comp drops out and the cch comes in but not in series with comp. It should be comp on NO contact and cch on NC contact. If not lease post some pics.
    Why not visit my website: www.rockncrystals.com.au ?

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Crankcase heater wired in series with compressor

    Some manufacturers do indeed use the compressor windings for oil heating in the off-mode.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Crankcase heater wired in series with compressor

    I have read about similar set ups on American style ac systems.

    Assuming the CCH is about 70W that works out at .3A at 230V so i don't think it will harm the compressor windings. Likewise the CCH would be about 755 ohms so another 3 or 4 ohms in the compressor winding won't make much difference.

    If you are concerned about the CCH shorting out and causing the compressor to run you could fit a small amperage fuse in line with the heater.
    Mostly found in Oxfordshire, UK :)

  5. #5
    Join Date
    Aug 2010
    Location
    Southeast Penna.
    Age
    31
    Posts
    26
    Rep Power
    0

    Re: Crankcase heater wired in series with compressor

    @Tesla it was a standard A/C compressor contactor (at least standard here in the US of A), no NC contact.

    @monkey spanners Those numbers make sense. I never had to mess with a crankcase heater so I didn't know how many watts they're supposed to draw. When you look at the ohm numbers though, that's definitely not a problem.

    Thanks for the info.

  6. #6
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    51
    Posts
    1,083
    Rep Power
    23

    Re: Crankcase heater wired in series with compressor

    Well I learnt something out of this post. Now I wonder why they all don't wire up like Jeremy said, could we just get away with a big 170ohm resistor monkey spanners and let the windings do the heating?
    Why not visit my website: www.rockncrystals.com.au ?

  7. #7
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Crankcase heater wired in series with compressor

    Copeland have a document with wiring diagrams....

    Www.hvacrinfo.com/ae_index.htm
    Scroll down to section 22 and select document 2-1230

    Sorry, can't master cut and paste on my new tablet yet.
    Last edited by Brian_UK; 15-05-2013 at 11:43 PM.
    Brian - Newton Abbot, Devon, UK