    Skope 2 doors freezer temperature issue



    Hi. I want to seek some help with the freezer that i am currenty use for the business. Back to few months ago, my freezer start to play up. The issue was the temperature always goes up and down which mean it can be -18c then the
    temperature only stay for 10 minutes then temperature start to goes up to -7c or -3c. Then an hour later, the temperature start went down to -12c then it went up again.

    I did call tech to inspect the freezer but they could not point out what cause the problem. I told him that if i replaced compressor, will it solve the problem but he replied not sure ( can be ). At the moment, i just leave the problem aside. I am suspect the temperature controller might be not working probably so it caused the temperature up and down.

    From my knowledge, compressor control the freezer, if it replace the new one, the problem should be fix. Is this right?



  2. #2
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    51
    Posts
    1,083
    Rep Power
    23

    Re: Skope 2 doors freezer temperature issue

    If you want to waste your money replace the compressor. Or you could take the advise of the technician you paid and take his advise or pay for more advise.
    If it ain't broke don't fux it
    Why not visit my website: www.rockncrystals.com.au ?

  3. #3
    Join Date
    May 2013
    Location
    Australia
    Posts
    3
    Rep Power
    0

    Re: Skope 2 doors freezer temperature issue

    I had call the company that supplied the freezer and they could not even told me where the problem was. They said maybe its compressor was getting old (6 yrs). Maybe i should call another tech to inspect the freezer..

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Skope 2 doors freezer temperature issue

    usually after 4 yr digital controller relays start to stick either closed contact- compressor chuggs its nuts off or led displays the signal to run but no power to the compressor, tapping the front on the controller should proove this. another way to proove this is to wire a standard mechanical stat and moniter the temperature- much cheaper than a pot change that can compound issues if it aint faulty- theres an aussie up near atherton queensland who is a master at fridges, as long as you pay ,as his tax man drives a ferrari- - other aussies are available for fridge work depending on what area you live in

  5. #5
    Join Date
    Sep 2012
    Location
    New Zealand
    Posts
    15
    Rep Power
    0

    Re: Skope 2 doors freezer temperature issue

    If it has an electronic controller, could be as simple as a dodgy (faulty) temp sensor probe. Especially if the temp is going up and down suddenly

  6. #6
    Join Date
    May 2013
    Location
    Australia
    Posts
    3
    Rep Power
    0

    Re: Skope 2 doors freezer temperature issue

    Maybe i should call my tech to change the temperature controller as its much cheaper to do it.

    Sadly.. my freezer playing up again .. Left door shows -17.9 and right door shows -7.4 degree..

    Thx for advice.....

  7. #7
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    51
    Posts
    1,083
    Rep Power
    23

    Re: Skope 2 doors freezer temperature issue

    Hi Smallwhale maybe you could call a different tech to check it out - sometimes two heads are better than one. You could have an intermittent fault which usually turn into permanent ones.