    Nov 2010
    Copenhagen
    45
    10
    Unisab II external 4-20mA signal, documentation needed.
    Hi all,
    I rewired an Unisab II yesterday, it had two 4-20mA signals in, one in 33, 34 and one in 47, 48 i believe.
    I needed to control the set point on the water, that worked well in 47, 48.
    What is the other input for?
    It was setup for weather compensation, but I changed that to external setpoint. The input in 47, 48 was a temp transducer in the pipe up the building. There are two chillers and a buffer tank.
    Does anybody have a manual and a wiring diagram on the unisab II?
    Regards,
    Peter
    Jun 2011
    Australia
    44
    336
    21
    Re: Unisab II external 4-20mA signal, documentation needed.
    Hi, I have a manual but not drawings. Private message me if you are interested.
    Nov 2010
    Copenhagen
    45
    10
    Message sent.
    Mar 2003
    uk
    57
    35
    Hi Petter 78
    Can you tell me what version UnisabII software is and if it is a screw or reciprocating compressor .
    Jan 2006
    Croatia
    68
    2,263
    31
    Hi, petter78
    Quote Originally Posted by petter78 View Post
    Hi all,
    Regards,
    Peter
    I was asking my friend electrician for assistance .... and he told me this ....
    32 - +24V
    33 - GND
    34 - 4-20mA
    are terminals for analog input for Volume slide position or outdoor temp compensation
    47-48 terminals are DI (digital input) start request feedback - if use remove jumper
    To control brine temperature there are terminals 25-26-27-28 for analog input of brine temperature from temperature sensor PT100 with scale -50C/+180C with 4 wires ...need to remove 100 Ohm resistor -capacity control must be set to .... CONTROL on BRINE ...
    or to use terminals for universal regulator (External input)
    37 - +24V
    38 - GND
    39 - 4-20mA signal
    and then make a calibration according to regulator used
    you can read about all above in the manual under compressor regulation chapter 6 received from HVACRsaurus
    Hope this will help a little ...
    Best regards, Josip
    Nov 2010
    Copenhagen
    45
    10
    Quote Originally Posted by Josip View Post
    Hi, petter78
    Best regards, Josip
    That helped a great deal. I was wrong about the terminals, it was not 47, 48 I used for external setpoint but 38, 39.
    All works like it should now. Earlier it was setup to use climatic control, but the signal send to 33, 34 related to wanted setpoint. No wonder it didn't work.
    Now I send a setpoint to 38, 39 that is already adjusted according to outside temperature.
    Thanks to all.
    /peter