    Unisab II external 4-20mA signal, documentation needed.



    Hi all,
    I rewired an Unisab II yesterday, it had two 4-20mA signals in, one in 33, 34 and one in 47, 48 i believe.
    I needed to control the set point on the water, that worked well in 47, 48.
    What is the other input for?
    It was setup for weather compensation, but I changed that to external setpoint. The input in 47, 48 was a temp transducer in the pipe up the building. There are two chillers and a buffer tank.

    Does anybody have a manual and a wiring diagram on the unisab II?

    Regards,
    Peter



  2. #2
    Join Date
    Jun 2011
    Location
    Australia
    Age
    44
    Posts
    337
    Rep Power
    21

    Re: Unisab II external 4-20mA signal, documentation needed.

    Hi, I have a manual but not drawings. Private message me if you are interested.

  3. #3
    Join Date
    Nov 2010
    Location
    Copenhagen
    Age
    45
    Posts
    10
    Rep Power
    0

    Re: Unisab II external 4-20mA signal, documentation needed.

    Message sent.

  4. #4
    Join Date
    Mar 2003
    Location
    uk
    Age
    57
    Posts
    35
    Rep Power
    0

    Re: Unisab II external 4-20mA signal, documentation needed.

    Hi Petter 78

    Can you tell me what version UnisabII software is and if it is a screw or reciprocating compressor .

  5. #5
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: Unisab II external 4-20mA signal, documentation needed.

    Hi, petter78

    Quote Originally Posted by petter78 View Post
    Hi all,
    I rewired an Unisab II yesterday, it had two 4-20mA signals in, one in 33, 34 and one in 47, 48 i believe.
    I needed to control the set point on the water, that worked well in 47, 48.
    What is the other input for?
    It was setup for weather compensation, but I changed that to external setpoint. The input in 47, 48 was a temp transducer in the pipe up the building. There are two chillers and a buffer tank.

    Does anybody have a manual and a wiring diagram on the unisab II?

    Regards,
    Peter
    I was asking my friend electrician for assistance .... and he told me this ....

    32 - +24V
    33 - GND
    34 - 4-20mA
    are terminals for analog input for Volume slide position or outdoor temp compensation


    47-48 terminals are DI (digital input) start request feedback - if use remove jumper


    To control brine temperature there are terminals 25-26-27-28 for analog input of brine temperature from temperature sensor PT100 with scale -50C/+180C with 4 wires ...need to remove 100 Ohm resistor -capacity control must be set to .... CONTROL on BRINE ...

    or to use terminals for universal regulator (External input)
    37 - +24V
    38 - GND
    39 - 4-20mA signal

    and then make a calibration according to regulator used

    you can read about all above in the manual under compressor regulation chapter 6 received from HVACRsaurus


    Hope this will help a little ...

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  6. #6
    Join Date
    Nov 2010
    Location
    Copenhagen
    Age
    45
    Posts
    10
    Rep Power
    0

    Re: Unisab II external 4-20mA signal, documentation needed.

    Quote Originally Posted by Josip View Post
    Hi, petter78



    I was asking my friend electrician for assistance .... and he told me this ....

    -
    -
    -
    -
    -

    you can read about all above in the manual under compressor regulation chapter 6 received from HVACRsaurus


    Hope this will help a little ...

    Best regards, Josip
    That helped a great deal. I was wrong about the terminals, it was not 47, 48 I used for external setpoint but 38, 39.

    All works like it should now. Earlier it was setup to use climatic control, but the signal send to 33, 34 related to wanted setpoint. No wonder it didn't work.

    Now I send a setpoint to 38, 39 that is already adjusted according to outside temperature.

    Thanks to all.

    /peter