    Transferring -33 deg C liquid ammonia



    Can anyone suggest maximum level in spare liquid receiver. Will transfer -33 C liquid into empty liquid receiver & will store it there for a period, so will warm up to ambient. When it warms it will expand, how much would be a safe level when adding the cold liquid?



  2. #2
    Join Date
    Nov 2009
    Location
    france
    Age
    64
    Posts
    225
    Rep Power
    19

    Re: Transferring -33 deg C liquid ammonia

    Hi Ranger,
    the volume will increase proportionally to liquid spec weight at -33 / liquid spec weight +??.
    I won't tell you more about the safe limit. In the company, a few years ago, a wrong recovering tank was delivered and was not according to the recovering procedure. the tank was overfilled and exploded. a motorway and a rest station had to be closed; many people evacuated to hospital for medical examinations. A bad story, so don't miss your calculation and if possible leave the relief valves fitted.

  3. #3
    Join Date
    Aug 2007
    Location
    Adelaide Australia
    Age
    70
    Posts
    562
    Rep Power
    24

    Re: Transferring -33 deg C liquid ammonia

    Hi Ranger
    Given it is -33 when you put it in the vessel without doing any calculations I wouldn't fill to more then 1/3 and if possible warm it up as you transfer, as cricri said make sure there are reliefs fitted and vented up high.
    Paul

  4. #4
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Transferring -33 deg C liquid ammonia

    Quote Originally Posted by PaulZ View Post
    Hi Ranger
    Given it is -33 when you put it in the vessel without doing any calculations I wouldn't fill to more then 1/3 and if possible warm it up as you transfer, as cricri said make sure there are reliefs fitted and vented up high.
    Paul
    Thanks, Its very tempting to fill it more, but as you say it will be probably 80% full when warmed up. Of course I will not fill it anymore due to being then overfull. An easy trap if not aware.

  5. #5
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Transferring -33 deg C liquid ammonia

    Hi Ranger.
    the specific volume increase from -35'C < +30'C is 12% for vapour ammonia.
    Last edited by Magoo; 09-05-2013 at 11:40 PM. Reason: correction

  6. #6
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Transferring -33 deg C liquid ammonia

    Hi, RANGER1

    Quote Originally Posted by RANGER1 View Post
    Can anyone suggest maximum level in spare liquid receiver. Will transfer -33 C liquid into empty liquid receiver & will store it there for a period, so will warm up to ambient. When it warms it will expand, how much would be a safe level when adding the cold liquid?

    Not sure, if you can do it, but maybe is better to empty system from HP receiver (transfer gas ammonia with compressor from -33 C separator to inter-cooler -10 C (if) then from inter-cooler separator to condenser and then empty from HP receiver) will take some time, but spare receiver you will fill with warm (environment temperature or little sub-cooled, if) liquid ammonia and then you can go up to 75-80% of the level within spare receiver ... there must be safety valve

    This is my suggestion (I did it on that way) ... no need to take care about liquid expansion and pressure increase when -33 C liquid come to environment temperature ... provide a high pressure hose for ammonia and connect one end to gas connection on the spare receiver and another end back to gas connection on separator -33 C or to gas connection on the inter-cooler -10 C ... with HP within receiver transfer will be very fast ...

    at -33 C liquid transfer there is a problem with flexible hoses too .... so I prefer to transfer warm ammonia ... 30 C/12 bar

    HP-high pressure

    No need to say ... be careful .... very careful .... check every connection more times ... before transfer you can check all transfer lines (liquid and gas) with high pressure gas ammonia from HP receiver for safety and for possible leaks ....

    This kind of work is very sensible and no need too many people around ... just need to be patient


    Good luck...

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  7. #7
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Transferring -33 deg C liquid ammonia

    Quote Originally Posted by Josip View Post
    Hi, RANGER1




    Not sure, if you can do it, but maybe is better to empty system from HP receiver (transfer gas ammonia with compressor from -33 C separator to inter-cooler -10 C (if) then from inter-cooler separator to condenser and then empty from HP receiver) will take some time, but spare receiver you will fill with warm (environment temperature or little sub-cooled, if) liquid ammonia and then you can go up to 75-80% of the level within spare receiver ... there must be safety valve

    This is my suggestion (I did it on that way) ... no need to take care about liquid expansion and pressure increase when -33 C liquid come to environment temperature ... provide a high pressure hose for ammonia and connect one end to gas connection on the spare receiver and another end back to gas connection on separator -33 C or to gas connection on the inter-cooler -10 C ... with HP within receiver transfer will be very fast ...

    at -33 C liquid transfer there is a problem with flexible hoses too .... so I prefer to transfer warm ammonia ... 30 C/12 bar

    HP-high pressure

    No need to say ... be careful .... very careful .... check every connection more times ... before transfer you can check all transfer lines (liquid and gas) with high pressure gas ammonia from HP receiver for safety and for possible leaks ....

    This kind of work is very sensible and no need too many people around ... just need to be patient


    Good luck...

    Best regards, Josip
    Thanks josip & everyone, unfortunately I had to remove approx 20 tonne of ammonia into empty cylinders in vacuum. Plant is being partially decommissioned within a time line, so cannot spend to much time doing it. The accumulator has plate freezers with no product, or load. I will used its liquid pump to transfer directly into empty cylinders, which each hold 2 tonne & can only be filled to 80% full, at ambient temperature. I had 2 days to do it, all ok filled cylinders to approx 50%. Will monitor levels as they are an ice block.

  8. #8
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Transferring -33 deg C liquid ammonia

    Defrost plates and get liquid above 0.0 C and only fill bottles to 30 % by weight.The volume will double at +20 C.

  9. #9
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Transferring -33 deg C liquid ammonia

    You get a 15% (give or take) increase from -30 to +30c Liquid NH3 and about 25% for upto 60C, so to be safe, fill your bottle at -33C to no more than 70%

  10. #10
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Transferring -33 deg C liquid ammonia

    Hi, RANGER1

    Quote Originally Posted by RANGER1 View Post
    Thanks josip & everyone, unfortunately I had to remove approx 20 tonne of ammonia into empty cylinders in vacuum. Plant is being partially decommissioned within a time line, so cannot spend to much time doing it. The accumulator has plate freezers with no product, or load. I will used its liquid pump to transfer directly into empty cylinders, which each hold 2 tonne & can only be filled to 80% full, at ambient temperature. I had 2 days to do it, all ok filled cylinders to approx 50%. Will monitor levels as they are an ice block.

    Time is quite short and job is big and very dangerous ... maybe you can drain ammonia into 2 or 3 cylinders in the same time (depending how many ammonia pumps you have available).

    Anyhow, good luck and take care ....

    Read my SIG, please ... last bottom row

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  11. #11
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Transferring -33 deg C liquid ammonia

    Quote Originally Posted by Josip View Post
    Hi, RANGER1




    Time is quite short and job is big and very dangerous ... maybe you can drain ammonia into 2 or 3 cylinders in the same time (depending how many ammonia pumps you have available).

    Anyhow, good luck and take care ....

    Read my SIG, please ... last bottom row

    Best regards, Josip
    josip, Ammonia cylinders have 2 25mm entry ports so no problem hooking up 2 hoses at once, thanks for advice.