Results 1 to 5 of 5
-
06-05-2013, 06:54 PM #1
Toshiba MMY-MAP1201HT8 H 02 faul code
Hi guys sorry to bother just want to ask about H 02 fault on Toshiba VRF MMY MAP 1201 HT 8 .... ?
So contractor working but no compressor wont start !!!
I am not sure if is boar faulty or compressor cos I check compressor and everything look normal on both ...
If anyone has the same problem please let me know how to diagnose more and be sure what exactly is wrong .
Thank You all
Cheers !
-
06-05-2013, 07:15 PM #2
Re: Toshiba MMY-MAP1201HT8 H 02 faul code
• Check compressor error.
• Check power voltage. (AC380–10%, 415V +10%).
• Check cable of compressor and phase-missing.
• Check connector/terminal connection on IPDU P.C. board.
• Check conduction of case heater.
(Check activation error due to liquid stagnation in compressor.)
• Check outdoor P.C. board (IPDU) error.
• Check outdoor MG-SW or OCR.
-
06-05-2013, 07:21 PM #3
Re: Toshiba MMY-MAP1201HT8 H 02 faul code
http://www.mediafire.com/view/?kqkx4zbk8bb3385
http://www.mediafire.com/view/?9xnhupyn7c3n04p
bit of literature for ya
-
06-05-2013, 07:27 PM #4
Re: Toshiba MMY-MAP1201HT8 H 02 faul code
Thanks a lot dude so If missing phase inverter board is faulty I guess .
-
06-05-2013, 07:37 PM #5
Re: Toshiba MMY-MAP1201HT8 H 02 faul code
it mentions theres a sub code to tell ya if its comp1 or 2- if its lost a phase then inv pcb should be protected, check correct power to outdoor- water in isolator,loose connections on circuit breakers