    Apr 2013
    Malaysia
    14
    Problem - Liquid Unable To Become Vapor During Suction
    Hi All, I'm not expert in Engineering Work,
    Currently I faced a big problem regarding liquid unable to become vapor during suction and some liquid will return to compressor.
    This screw compressor was a 90HP's Chiller Medium Temp Compressor with Old Multi-System and MODIFIED to 150HP's Freezer Low Temp Compressor with 4 Blowers Currently, Temperature can up to -25'C.
    Will this problem link to orific, expansion valve or suction accumulator?
    Hope everyone could lend me a hand to solve this problem.
    Thanks...
    Apr 2011
    India
    94
    14
    Re: Problem - Liquid Unable To Become Vapor During Suction
    How u come to know that liquid refrigerant is entering in the compressor ? As per my knowledge, the amount of the refrigerant entering the evaporator is not properly controlled(which is dependent on the load on chiller).Hence the problem is associated with orifice.
    Sep 2012
    New Zealand
    Are you sure liquid is coming back to compressor? Ice on suction line and compressor is normal as suction line temp will be below 0°c, this does not mean floodback.
    If it is floodback, fault will be either expansion valve is faulty, feeding too much refrigerant for some reason. Or evaporator is not absorbing enough heat load from room, due to faulty fans or iced up.
    Apr 2013
    Malaysia
    14
    Quote Originally Posted by Sumit View Post
    Hi, Thanks for your reply,
    Because the noises from compressor, so I suspect that liquid return to compressor.
    Besides, the model for the compressor is Bitzer OSN-7471K with economizer system, will this system affect the floodback?
    Oct 2012
    Russia
    42
    392
    Provide data: SH, SC, DSH, current on full load, delta T in and out.
    Expansion valve of economizer system can be locked in one position.
    Apr 2001
    79
    5,071
    35
    Split Croatia
    6,151
    Quote Originally Posted by hongyunref View Post
    Thanks...
    Have you got installed suction accumulator on that circuit?
Tags for this Thread