    Problem - Liquid Unable To Become Vapor During Suction



    Hi All, I'm not expert in Engineering Work,

    Currently I faced a big problem regarding liquid unable to become vapor during suction and some liquid will return to compressor.

    This screw compressor was a 90HP's Chiller Medium Temp Compressor with Old Multi-System and MODIFIED to 150HP's Freezer Low Temp Compressor with 4 Blowers Currently, Temperature can up to -25'C.

    Will this problem link to orific, expansion valve or suction accumulator?

    Hope everyone could lend me a hand to solve this problem.

    Thanks...



  2. #2
    Join Date
    Apr 2011
    Location
    India
    Age
    36
    Posts
    94
    Rep Power
    13

    Re: Problem - Liquid Unable To Become Vapor During Suction

    Hi,

    How u come to know that liquid refrigerant is entering in the compressor ? As per my knowledge, the amount of the refrigerant entering the evaporator is not properly controlled(which is dependent on the load on chiller).Hence the problem is associated with orifice.

  3. #3
    Join Date
    Sep 2012
    Location
    New Zealand
    Posts
    15
    Rep Power
    0

    Re: Problem - Liquid Unable To Become Vapor During Suction

    Are you sure liquid is coming back to compressor? Ice on suction line and compressor is normal as suction line temp will be below 0°c, this does not mean floodback.
    If it is floodback, fault will be either expansion valve is faulty, feeding too much refrigerant for some reason. Or evaporator is not absorbing enough heat load from room, due to faulty fans or iced up.

  4. #4
    Join Date
    Apr 2013
    Location
    Malaysia
    Posts
    14
    Rep Power
    0

    Re: Problem - Liquid Unable To Become Vapor During Suction

    Quote Originally Posted by Sumit View Post
    Hi,

    How u come to know that liquid refrigerant is entering in the compressor ? As per my knowledge, the amount of the refrigerant entering the evaporator is not properly controlled(which is dependent on the load on chiller).Hence the problem is associated with orifice.
    Hi, Thanks for your reply,
    Because the noises from compressor, so I suspect that liquid return to compressor.
    Besides, the model for the compressor is Bitzer OSN-7471K with economizer system, will this system affect the floodback?

  5. #5
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: Problem - Liquid Unable To Become Vapor During Suction

    Provide data: SH, SC, DSH, current on full load, delta T in and out.
    Expansion valve of economizer system can be locked in one position.

  6. #6
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: Problem - Liquid Unable To Become Vapor During Suction


  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Problem - Liquid Unable To Become Vapor During Suction

    Quote Originally Posted by hongyunref View Post

    Will this problem link to orific, expansion valve or suction accumulator?


    Thanks...
    Have you got installed suction accumulator on that circuit?