    Help with TXV selection



    Customer requesting a txv for 50*f liquid. Its a somewhat clouded message because in another email they asked for a 50*f subcooled valve. Can anyone shed some light for me here or do I need more info from them.. As always, thanks guys.. Kengineering



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Help with TXV selection

    to choose the right TXV you will need more info than what you have such as: type of refrigerant, evaporating capacity, cooling capacity, room temp, pressure drop,

    Every TXV catalog will give you the right info.

  3. #3
    Join Date
    Jan 2007
    Location
    India
    Posts
    65
    Rep Power
    19

    Re: Help with TXV selection

    Hi,
    Refer the attached Danfoss catalogue page which explains the selection procedure of TXV.

    Regards,
    Sendhil