    Hello guys,
    New here, but long in the job...
    Are there any circumstances under which 134a is flammable? Someone is trying to say it is, with a certain % of air, but I've never heard this.
    Jun 2005
    California
    395
    Re: R134a
    Quote Originally Posted by terminator
    Hello guys,
    The following is from MSDS :
    HFC-134a is not flammable in air at temperatures up to
    100 deg. C (212 deg. F) at atmospheric pressure. However, mixtures of HFC-134a with high concentrations of air at elevated pressure and/or temperature can become combustible in the presence of an ignition source. HFC-134a can also become combustible in an oxygen enriched environment
    (oxygen concentrations greater than that in air). Whether a mixture containing HFC-134a and air, or HFC-134a in an oxygen enriched atmosphere become combustible depends on
    the inter-relationship of 1) the temperature 2) the
    pressure, and 3) the proportion of oxygen in the mixture. In general, HFC-134a should not be allowed to exist with air above atmospheric pressure or at high temperatures; or in an oxygen enriched environment. For example HFC-134a should NOT be mixed with air under pressure for leak testing or other purposes.
    Feb 2006
    Hampshire
    61
    Re: R134a
    Thanks for that.....
    Jan 2006
    Port Adelaide
    52
    Re: R134a
    Hi terminator.
    Today at work I was sweating an accumulator. When I took it off and went to trow it on the ground, a 2 foot flame shot out the end.
    This was 134a. But it was the oil and UV dye that caused the flame. Bloody phosgene burns the nose and eyes.
  1. R507 in an R134a compressor: any danger?
    Last Post: 21-12-2009, 01:44 AM
  2. R12 to R134a
    By fireblade in forum Domestic
    Last Post: 19-08-2006, 09:02 PM
  3. Pressure Transmitter R134a Setpoints
    By cooltrain in forum Technical Speculations
    Last Post: 28-02-2005, 10:05 AM
  4. Replies: 5
    Last Post: 01-03-2004, 10:59 PM
  5. R507 in an R134a compressor: system design
    Last Post: 01-05-2003, 09:25 AM