Thread: McQuay ALS SE344.3ST134
-
26-04-2013, 11:35 AM #1
McQuay ALS SE344.3ST134
Hii.. to all Please help me,i have problem from chiller McQuay Unit 3 Control Alarm Freeze Alarm Whats Problem?What's Componen it's faulty?please give my solution problem?if you have Wirring Diagram please send me to email
Last edited by frank; 21-10-2013 at 07:06 PM.
-
26-04-2013, 11:49 AM #2
Re: McQuay ALS SE344.3ST134
Freeze up prevention alarm?
Probably not a component at all, have you checked the water flow and the water inlet / outlet temperatures?
-
26-04-2013, 02:03 PM #3
Re: McQuay ALS SE344.3ST134
any have wirring diagram PCO 2 CAREL FOR Chiller McQuay ALS SE344
please send me in email
Thx all...Last edited by frank; 21-10-2013 at 07:06 PM.
-
21-10-2013, 06:21 PM #4
Re: McQuay ALS SE344.3ST134
You should check Leaving water sensor.If temp goes beyond a Freeze set point Alarm then this alarm occurs