    how to know the estimation of Electrical Power Consumption (kW)



    Hi,

    Greetings and I am new here, previously I work as Industrial Automation and Electrical Engineer but now im moving into HVAC field. This is completely new for me.

    I am now working in a project of HVAC, Here some of the calculation i've done ;

    OAHU-1
    154800 Kcal/H
    10500 CMH
    516 L/min

    AHU-1
    16340 Kcal/H
    14500 CMH
    54.5 L/min

    AHU-2
    26660 Kcal/H
    13300 CMH
    89 L/min

    I have found the formula to convert Kcal/H to kW
    for example AHU-1
    16340 / 5 = 3668
    then
    3668 / 60 = 54.5 kW (but this is not Electrical Motor Power Consumption)

    How to calculate the estimation of Electrical motor Power Consumption (kW) ?

    Thank you



  2. #2
    Join Date
    Dec 2011
    Location
    Brazil
    Posts
    2
    Rep Power
    0

    Re: how to know the estimation of Electrical Power Consumption (kW)

    16340 Kcal/H = 19Kw, not 54.5kW
    http://www.convertworld.com/en/power/

    The electrical motor power consumption will be 19Kw * 3.41214 / EER
    For example, if the EER = 11 then the consumption in this example will be 5.9kW
    http://en.wikipedia.org/wiki/Seasona...ficiency_Ratio