    high pressure switch and solenoid valve



    hi
    i have lg 24000 btu split ac unit
    there is high pressure switch and solenoid valve
    Snap_2013.04.25_20h00m01s_001.jpg

    the both the solenoid valve and hi pressure switch wired togather
    the hi press switch installed on the suction pipe of condenser
    the sloenoid installed between evaporator inlet and the discharge of the compressor
    what is the utility of them
    they printed on the hi pressure switch
    ON 32 KGF/CM2 G
    OFF 26 KGF/32 G
    DSC_2188(01).jpg
    Last edited by kefah; 28-04-2013 at 02:42 PM.



  2. #2
    Join Date
    Jan 2011
    Location
    england
    Posts
    57
    Rep Power
    15

    Re: high pressure switch and solenoid valve

    What do you mean how do they work? Are you sure the solenoid is on the suction?

  3. #3
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    36
    Posts
    623
    Rep Power
    17

    Re: high pressure switch and solenoid valve

    Quote Originally Posted by bigspee View Post
    What do you mean how do they work? Are you sure the solenoid is on the suction?
    no the the sloenoid installed between evaporator inlet and the discharge of the compressor

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: high pressure switch and solenoid valve

    Sounds like an over pressure relief system.

    If the condensing pressure goes too high it relieves the pressure directly into the evaporator for return to the compressor.

    Some chillers do this with a pressure relief valve instead of the solenoid valve.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    36
    Posts
    623
    Rep Power
    17

    Re: high pressure switch and solenoid valve

    Quote Originally Posted by Brian_UK View Post
    Sounds like an over pressure relief system.

    If the condensing pressure goes too high it relieves the pressure directly into the evaporator for return to the compressor.

    Some chillers do this with a pressure relief valve instead of the solenoid valve.
    thank you man

  6. #6
    Join Date
    May 2013
    Location
    slovakia
    Age
    36
    Posts
    4
    Rep Power
    0

    Re: high pressure switch and solenoid valve

    This is a safety pressure switch contact when there is enough amount of ***** pressure ..and dis contact when there is a leak in the ***** and a pressure decrease ...

  7. #7
    Join Date
    Jul 2006
    Location
    uk
    Age
    46
    Posts
    46
    Rep Power
    0

    Re: high pressure switch and solenoid valve

    Could be a hot gas bypass for when inverter is running flat out and suction is low and discharge is high, levels the system out a bit!

  8. #8
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    36
    Posts
    623
    Rep Power
    17

    Re: high pressure switch and solenoid valve

    the right answer is by Brian_UK
    Sounds like an over pressure relief system.

    If the condensing pressure goes too high it relieves the pressure directly into the evaporator for return to the compressor.

    Some chillers do this with a pressure relief valve instead of the solenoid valve.