Results 1 to 7 of 7

Thread: ahu coil tev

  1. #1
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    ahu coil tev



    looked at a Ahu today unit has 4 coils but only 2 tevs outlet from valve was teed off to 2 coils I think it might work better with 4 tevs
    Attached Images Attached Images



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: ahu coil tev

    nice drawing haha
    tev's should be sized for the system anyway, if it works dont maul, fitting 4 tev's and running bulbs and by the time u run all ur pipework you wont be able to get in the ahu and if u do do it, no doubt the pipes will vibrate and chaff through

  3. #3
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: ahu coil tev

    the problem is out let temp from coils is not balanced one is at -4 and one is at +9 as there is no control where the refrigerant goes after the valve so you can not set the super heat correctly for each coil. space to fit valves is not a issue as the units are 240kw units the problem is part of the coils are icing and parts of the coils are not very cold

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: ahu coil tev

    Go for it then, maybe fit liq line solonoids and sight glasses to stage ur cooling. Hope ur pipework is better than ur drawing

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: ahu coil tev

    What part of the country is the installation Martin?

    Only asking because I did something similar and mine worked fine at commissioning stage but as I haven't been back to the job for 2 years, you may be looking at my work

  6. #6
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: ahu coil tev

    Hertfodshire the drawing is the best you get with windows 8 lol

  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: ahu coil tev

    I'll post a couple of photo's then lol