Thread: ahu coil tev
    Feb 2008
    386
    13
    ahu coil tev
    looked at a Ahu today unit has 4 coils but only 2 tevs outlet from valve was teed off to 2 coils I think it might work better with 4 tevs
    Oct 2007
    manchester
    44
    5,707
    Re: ahu coil tev
    nice drawing haha
    tev's should be sized for the system anyway, if it works dont maul, fitting 4 tev's and running bulbs and by the time u run all ur pipework you wont be able to get in the ahu and if u do do it, no doubt the pipes will vibrate and chaff through
    Feb 2008
    386
    13
    Re: ahu coil tev
    the problem is out let temp from coils is not balanced one is at -4 and one is at +9 as there is no control where the refrigerant goes after the valve so you can not set the super heat correctly for each coil. space to fit valves is not a issue as the units are 240kw units the problem is part of the coils are icing and parts of the coils are not very cold
    Oct 2007
    manchester
    44
    5,707
    Re: ahu coil tev
    Go for it then, maybe fit liq line solonoids and sight glasses to stage ur cooling. Hope ur pipework is better than ur drawing
    Oct 2001
    Nottingham UK
    5,117
    42
    Re: ahu coil tev
    What part of the country is the installation Martin?
    Only asking because I did something similar and mine worked fine at commissioning stage but as I haven't been back to the job for 2 years, you may be looking at my work
    I'm back on the Pale
    Feb 2008
    386
    13
    Re: ahu coil tev
    Hertfodshire the drawing is the best you get with windows 8 lol
    Oct 2001
    Nottingham UK
    5,117
    42
    Re: ahu coil tev
    I'll post a couple of photo's then lol