    haveing some problems with TUSCAN?



    I am new at elm so please excuse me!

    It has 5 sensors
    Aie on air off
    Evp on evp off
    Defrost
    PROBLEM 1
    My question is evp on and off control the superheat? Yes
    If so where do you set it
    And air on and off control capacity yes?
    PROBLEM 2
    When I connect hand held to one it connect very quickly and on second it counts from 1 to 250 and restarts again and there is no display and valve is not clicking but it was doing it day before when I switched it off these are ex-supper market unit so I can learn so thing new



  2. #2
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: haveing some problems with TUSCAN?

    Super heat is set by controller, should be 6k, air on/off is control, can be set to 100% air off or any % in between. check the plug/socket on the unit not connecting, if it persists could be a bad joint etc.

    alec
    Mostly found in the southern part of this green and pleasant land.

  3. #3
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: haveing some problems with TUSCAN?

    I've had the handset not working when plugged into the display but fine when plugged directly into the controller.

    Radford Control Services run the show now. They used to have info on the product on theor site but just had a look and it appears it's in the process of being updated.

    Cheers,
    Andy.
    Health and safety first..........unless I'm in a hurry.

  4. #4
    Join Date
    Aug 2011
    Location
    yorkshire
    Posts
    40
    Rep Power
    0

    Re: haveing some problems with TUSCAN?

    Air on/off controlls what part of valve?
    i want to reduse prussure in evp by 20 psi what should i ajust?
    you guys thanks for the help

  5. #5
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: haveing some problems with TUSCAN?

    The controller only affects the expansion valve, air on/off is for themostat control (cabinet temperature). Suction pressure is affected by compressor control, if you have a Tuscan fitted adjust the pressure cut out for the compressors.

    alec
    Mostly found in the southern part of this green and pleasant land.

  6. #6
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: haveing some problems with TUSCAN?

    Been a while but I recall there a a few types of the controllers but a main difference is the type of expansion valve. One type has a relay to energise a LLSV and the other a solid state jobbie to pulse an AKV or similar.

    Like Al says, this wont alter pressue in evaporator as this is set by the compressor/pack controller. Just lets refrigerant into the coil.

    Cheers,
    Andy.
    Health and safety first..........unless I'm in a hurry.

  7. #7
    Join Date
    May 2004
    Location
    UK
    Posts
    71
    Rep Power
    20

    Re: haveing some problems with TUSCAN?

    Superheat default is 8 degrees (HT) and 6 degrees (LT). The setting can be changed, but from memory the controllers don't like it.
    I have some ELM PDF files that I can mail you if you let me have an e.mail address to send them to.

    Nick