    Confusing The Calculation Part Between Refrigerant's Superheat and Sub cooling



    Hi All,

    I'm new to learn and gain knowledge in this industry and currently facing a problem regarding the calculation part for refrigerant's superheat and sub cooling,

    I searched few ways to calculate but answers that I get is different.

    As other website suggested, I get these information to calculate superheat and sub cooling:

    Suction Line Temperature: 4'C/39.2'F
    Suction Line Pressure: 32psi / 17.30psig

    Liquid Line Temperature: 41.5'C/106.7'F
    Liquid Line Pressure: 230psi / 215.30psig

    Indoor Temperature: 3.5'C/38.3'F
    Outdoor Temperature: 27'C/80.6'F

    Additionally, is superheat and sub cooling can indicate us the way to control humidity (RH%) in the cleanroom? Because current RH in cleanroom is excess that the RH required.

    Thanks...



  2. #2
    Join Date
    May 2011
    Location
    India
    Age
    32
    Posts
    72
    Rep Power
    7

    Re: Confusing The Calculation Part Between Refrigerant's Superheat and Sub cooling

    Its related to the refrigerent PT chart.

    Subcooling has nothing to do with the RH maintanance. ADP of the cooling coil does. Lower the ADP to reduce the RH!

  3. #3
    Join Date
    Apr 2013
    Location
    Malaysia
    Posts
    12
    Rep Power
    0

    Re: Confusing The Calculation Part Between Refrigerant's Superheat and Sub cooling

    Hi,
    Really Thanks For Your Advice,
    From The PT Chart That Sir Advice, I Should Refer The Temperature To Get Psig or From Psig To Get Temperature?

  4. #4
    Join Date
    Aug 2006
    Location
    Spencer ma.
    Age
    53
    Posts
    109
    Rep Power
    12

    Re: Confusing The Calculation Part Between Refrigerant's Superheat and Sub cooling

    Read - 101- it will help you with super-heat and sub cooling.
    Last edited by tonyhavcr; 30-04-2013 at 02:49 AM.

  5. #5
    Join Date
    May 2011
    Location
    India
    Age
    32
    Posts
    72
    Rep Power
    7

    Re: Confusing The Calculation Part Between Refrigerant's Superheat and Sub cooling

    Quote Originally Posted by hongyunref View Post
    Hi,
    Really Thanks For Your Advice,
    From The PT Chart That Sir Advice, I Should Refer The Temperature To Get Psig or From Psig To Get Temperature?
    No, with the pressure gauge installed in the suction line, see the pressure gauge reading. Now, see the PT chart of the corrosponding refrigerent and see that particular pressure gauge reading, what is the temperature indicated in the chart.
    Nom measure the temperature at the suction line where it enter the compressor (inlet of the condensing unit). Difference between these temperature will give you the value of refrigerent super heat.

  6. #6
    Brian_UK's Avatar
    Brian_UK is online now Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    69
    Posts
    10,381
    Rep Power
    49

    Re: Confusing The Calculation Part Between Refrigerant's Superheat and Sub cooling

    Also, read Parker/Sporlan Using the PT Chart as a service tool.

    Download article reference 10-135.

    http://www.parker.com/portal/site/PA...put=Literature
    Brian - Newton Abbot, Devon, UK
    Retired March 2015