Results 1 to 12 of 12
Thread: Make sense of these measurments
31-01-2006, 12:42 PM #1
Multideck cabinet runs at 0 c to +2c
134a, cap tube and small pipe runs. (unit is only 6' wide)
I have just obtained these measurements. Please give feedback on them. ( unit is running down to temp ok)
ambient temp 16 c
Compressor suction temp (gauge) -15c
Comp discharghe temp (gauge) 33c
Tube temp straight out of compressor 52c
Tube temp entering condenser (after running through dry defrost tray) 30c
Tube temp out of condenser 24c
Tube temp out of evap 14c
Suction tube temp 6" from compressor 14c
31-01-2006, 01:00 PM #2
Re: Make sense of these measurments
[QUOTE=shark26]Multideck cabinet runs at 0 c to +2c
ambient temp 16 c
SST -15c
SDT 33c
Discharge 52c
LLT 24c
evap exit 14c
9K sub cooling
29K superheat
31-01-2006, 01:10 PM #3
And what do you make of these values??
31-01-2006, 01:37 PM #4
Both look very high.
For that type of appliction I would have thought more along the lines of 3K subcooling and 15K superheat.
What are the velocities of your air curtain?
What happens when you load the unit?
How long does it take to pull down?
How long are the cycles?
What type of defrost?
What are the times of defrost?
31-01-2006, 01:42 PM #5
they seem about average. ( compared to others on test.)
31-01-2006, 01:44 PM #6
Wow. Be interesting to see what the other guys rekon. I'd love to get my hands on one and gut it just to see what it does.
31-01-2006, 04:34 PM #7
Have just put a weight charge into cabinet
1.075Kg 134a
New figures
SST -12 c
SDT 35 c
Discharge 52 c
LLT 30 c
Evap exit 13
Ambient temp 18 c
(condenser air input 18 c)
air output 27 c)
Superheat 5k
subcooling 25k
31-01-2006, 04:37 PM #8
Originally Posted by hybridjunction
08-02-2006, 08:52 AM #9
13-02-2006, 06:55 AM #10
lol don't give up mate. Hey did you give that charging method a crack??
On that cabinet mate I reckon on a cap tube you should have 9k subcooling and maybe 10-12k total superheat. To get it just right you need 0k superheat on the evap
14-02-2006, 08:43 AM #11
Hi hybridjunction, yes i did give the chrging method a go and yes it did work. dragged the gas back out and is was accurate. Thanks for all the advise mate.
15-02-2006, 11:28 AM #12
No probs mate. Glad to help.
Make a Recovery Unit
By shark26 in forum Tools and CalculatorsReplies: 12Last Post: 22-02-2009, 06:49 PM -
I want to make a room: 14',9',9' cool
By audioaddict in forum Air ConditioningReplies: 11Last Post: 10-08-2006, 12:15 AM -
started to make an evap for my chiller
By The MG Pony in forum FundamentalsReplies: 8Last Post: 22-07-2006, 08:44 PM -
Best way to sense level of liquid refrigerant in receiver?
By star882 in forum FundamentalsReplies: 2Last Post: 16-11-2005, 05:34 PM -
Does anyone make these?
By Daddy Cool in forum Air ConditioningReplies: 2Last Post: 14-02-2005, 06:28 AM