    Make sense of these measurments



    Multideck cabinet runs at 0 c to +2c
    134a, cap tube and small pipe runs. (unit is only 6' wide)

    I have just obtained these measurements. Please give feedback on them. ( unit is running down to temp ok)
    ambient temp 16 c

    Compressor suction temp (gauge) -15c
    Comp discharghe temp (gauge) 33c
    Tube temp straight out of compressor 52c
    Tube temp entering condenser (after running through dry defrost tray) 30c
    Tube temp out of condenser 24c
    Tube temp out of evap 14c
    Suction tube temp 6" from compressor 14c




  2. #2
    Join Date
    Jan 2006
    Location
    Port Adelaide
    Posts
    52
    Rep Power
    19

    Re: Make sense of these measurments

    [QUOTE=shark26]Multideck cabinet runs at 0 c to +2c

    ambient temp 16 c
    SST -15c
    SDT 33c
    Discharge 52c
    LLT 24c
    evap exit 14c



    9K sub cooling
    29K superheat

  3. #3
    Join Date
    Jan 2006
    Location
    UK
    Posts
    54
    Rep Power
    19

    Re: Make sense of these measurments

    And what do you make of these values??

  4. #4
    Join Date
    Jan 2006
    Location
    Port Adelaide
    Posts
    52
    Rep Power
    19

    Thumbs up Re: Make sense of these measurments

    Both look very high.


    For that type of appliction I would have thought more along the lines of 3K subcooling and 15K superheat.

    What are the velocities of your air curtain?

    What happens when you load the unit?
    How long does it take to pull down?
    How long are the cycles?
    What type of defrost?
    What are the times of defrost?

    Last edited by hybridjunction; 31-01-2006 at 01:41 PM.

  5. #5
    Join Date
    Jan 2006
    Location
    UK
    Posts
    54
    Rep Power
    19

    Re: Make sense of these measurments

    they seem about average. ( compared to others on test.)
    ?

  6. #6
    Join Date
    Jan 2006
    Location
    Port Adelaide
    Posts
    52
    Rep Power
    19

    Re: Make sense of these measurments

    Wow. Be interesting to see what the other guys rekon. I'd love to get my hands on one and gut it just to see what it does.

  7. #7
    Join Date
    Jan 2006
    Location
    UK
    Posts
    54
    Rep Power
    19

    Re: Make sense of these measurments

    Have just put a weight charge into cabinet
    1.075Kg 134a

    New figures
    SST -12 c
    SDT 35 c
    Discharge 52 c
    LLT 30 c
    Evap exit 13

    Ambient temp 18 c

    (condenser air input 18 c)
    air output 27 c)

    Superheat 5k
    subcooling 25k


  8. #8
    Join Date
    Jan 2006
    Location
    UK
    Posts
    54
    Rep Power
    19

    Re: Make sense of these measurments

    Quote Originally Posted by hybridjunction
    Wow. Be interesting to see what the other guys rekon. I'd love to get my hands on one and gut it just to see what it does.
    The have perforated back panels which lets cold air pass over shelves. Also has vent on top which gives a sort of air curtain...

  9. #9
    Join Date
    Jan 2006
    Location
    UK
    Posts
    54
    Rep Power
    19

    Re: Make sense of these measurments

    Quote Originally Posted by hybridjunction
    Wow. Be interesting to see what the other guys rekon.
    Obviously nothing

  10. #10
    Join Date
    Jan 2006
    Location
    Port Adelaide
    Posts
    52
    Rep Power
    19

    Re: Make sense of these measurments

    lol don't give up mate. Hey did you give that charging method a crack??

    On that cabinet mate I reckon on a cap tube you should have 9k subcooling and maybe 10-12k total superheat. To get it just right you need 0k superheat on the evap

  11. #11
    Join Date
    Jan 2006
    Location
    UK
    Posts
    54
    Rep Power
    19

    Re: Make sense of these measurments

    Hi hybridjunction, yes i did give the chrging method a go and yes it did work. dragged the gas back out and is was accurate. Thanks for all the advise mate.

  12. #12
    Join Date
    Jan 2006
    Location
    Port Adelaide
    Posts
    52
    Rep Power
    19

    Re: Make sense of these measurments

    No probs mate. Glad to help.

Similar Threads

  1. Make a Recovery Unit
    By shark26 in forum Tools and Calculators
    Replies: 12
    Last Post: 22-02-2009, 06:49 PM
  2. I want to make a room: 14',9',9' cool
    By audioaddict in forum Air Conditioning
    Replies: 11
    Last Post: 10-08-2006, 12:15 AM
  3. started to make an evap for my chiller
    By The MG Pony in forum Fundamentals
    Replies: 8
    Last Post: 22-07-2006, 08:44 PM
  4. Replies: 2
    Last Post: 16-11-2005, 05:34 PM
  5. Does anyone make these?
    By Daddy Cool in forum Air Conditioning
    Replies: 2
    Last Post: 14-02-2005, 06:28 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •