    Oct 2003
    56
    5,519
    28
    Avoiding excessive pressure
    Subcritical setup, R134a/CO2 VIAA BPHE.
    At standstill, a CO2 can face excessive high pressure when ambient rises.
    Therefore, a separate small cooling unit (power by a small generator) is connected to a coil, submerged in the CO2 liquid receiver. This maintains a safe pressure < 40 bar.
    But, I have now the following idea. The CO2 flows out of the BPHE, kept by the 134a at -10C. If we're sure we keep the BPHE always at -10C, even at CO2 standstill, then we have just above the receiver a point which can reduce excessive pressure without a separate unit.
    Am I correct?
    Mar 2006
    Merate (LC) - Italy
    47
    2,553
    Re: Avoiding excessive pressure
    Yes, in Danmark I've seen frequently liquid receivers/flash tanks and other refr.components inside of the cold rooms
    Oct 2012
    Russia
    36
    391
    12
    Dont understand some little words like BPHE)
    44
    3,800
    38
    Quote Originally Posted by RusBuka View Post
    I believe its brazed plate heat exchanger.
    Oct 2003
    56
    5,519
    28
    Mmmm, NNN not a bad idea but what about PED at all? Why not install it directly in the freezer itself?
    But I was thinking that the R134a always-running-cascadecondensor acts also a safety device to limit pressure in the receiver at 26 bar (-10C) because this will be always the coldest point above the receiver.
    I was surprised all the necessary items are cheaper than expected.
    Indeed, BPHE a brazed plate heat exchanger.
    Mar 2010
    usa
    40
    119
    11
    I was thinking about this also, My concern is would the B.P.H.E. remove enough BTU's to keep the pressure low at a stand still?
    Mar 2006
    Merate (LC) - Italy
    47
    2,553
    I can't see any conflict between PED and installing a liquid receiver in the cold room.
    For what concerns R134a high side preventing boiling in the low side, it's not effective in case of power failure. That's the main reason why the low side shall be kept cold at all times.