    Mar 2012
    United Kingdom
    42
    63
    13
    Question Carrier 30 XA high pressure
    Hi Guys just want make sure if I am right with High Pressure diagnose on CARRIER 30 XA water chiller . So all fans are Ok ambient temperature is 10 degrees and after 5 - 6 hours chiller stop working cos of HP . All condenser and fans are OK but I found small leak on pressure relief valve see picture ...
    It could be problem with refrigeration or not really ....
    BTW chiller when is starting is so NOISY with hissing noise .
    Thanks 4 any advice
    May 2013
    Pakistan
    35
    5
    Re: Carrier 30 XA high pressure
    please reset the high pressure switch mounted on compressor high pressure line.
    Oct 2007
    manchester
    5,639
    45
    Apr 2009
    israel
    778
    check your hp sensor , this could leed to problems as you discribe , expecially if unit works well for 5 hours!
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!
    Oct 2009
    merida mexico
    282
    15
    the machine has electric valves on the discharge?