    Question Carrier 30 XA high pressure



    Hi Guys just want make sure if I am right with High Pressure diagnose on CARRIER 30 XA water chiller . So all fans are Ok ambient temperature is 10 degrees and after 5 - 6 hours chiller stop working cos of HP . All condenser and fans are OK but I found small leak on pressure relief valve see picture ...


    It could be problem with refrigeration or not really ....

    BTW chiller when is starting is so NOISY with hissing noise .



    Thanks 4 any advice


    Cheers
    Attached Images Attached Images



  2. #2
    Join Date
    May 2013
    Location
    Pakistan
    Age
    35
    Posts
    5
    Rep Power
    0

    Re: Carrier 30 XA high pressure

    please reset the high pressure switch mounted on compressor high pressure line.

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

  4. #4
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    18

    Re: Carrier 30 XA high pressure

    Hi
    check your hp sensor , this could leed to problems as you discribe , expecially if unit works well for 5 hours!
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  5. #5
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: Carrier 30 XA high pressure

    the machine has electric valves on the discharge?