Results 1 to 4 of 4

Thread: Citymulti

  1. #1
    Join Date
    May 2008
    Location
    dublin
    Posts
    80
    Rep Power
    17

    Citymulti



    I have a city multi p125 and 2 indoors p63s with one par 31 remote .the remote cable was never looped in ,can I change settings with a par 27 remote to get both units to run and then take off par 27 back off system if so how or will I just need to run a new cable
    cheers



  2. #2
    Join Date
    Mar 2009
    Location
    Uk
    Age
    41
    Posts
    121
    Rep Power
    17

    Re: Citymulti

    You need to run a new cable if you want to use the PAR 30.

  3. #3
    Join Date
    Mar 2011
    Location
    Singapore
    Posts
    212
    Rep Power
    16

    Re: Citymulti

    Unfortunately when there is no centralized controller or system controller, ME an MA remote controller can not be used together in a system. Bet is to use all either ME or MA. Of course you need to run a loop (TB15) cable for grouping with MA. ME plus point is that you need not to run extra cable for such situation.

  4. #4
    Join Date
    May 2008
    Location
    dublin
    Posts
    80
    Rep Power
    17

    Re: Citymulti

    Cheers joe . Just going to run a loop in . Had just heard that if I hook a par 27 up to one of the indoors I could tell it it has the same remote address and take the par 27 back off so I wouldn't have to run the loop.

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •