    Mitsubishi PUHZ-P100VHA2-UK ACTM board keeps blowing!



    I have recently been having ongoing problems with this unit, recently fitted a new power board and noise filter board. Returned yesterday to fit ACTM board, switched on, compressor started to run so sat in van, when I came back found had tripped and ACTM board had blown again, I do however have a spare ACTM board on van. I've fitted it and wanted to find out if power board has gone too so I've powered it up and the 2 led's have lit so no other damage but I quickly powered it down just incase. The only thing I can think of is the compressor is faulty but don't want to try it or disconnect it incase the board blows again, any suggestions???! It's single phase.



  2. #2
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: Mitsubishi PUHZ-P100VHA2-UK ACTM board keeps blowing!

    ACTM board what is that?

  3. #3
    Join Date
    Apr 2013
    Location
    England
    Posts
    4
    Rep Power
    0

    Re: Mitsubishi PUHZ-P100VHA2-UK ACTM board keeps blowing!

    A small board approx 3 inches squared connects to power board

  4. #4
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: Mitsubishi PUHZ-P100VHA2-UK ACTM board keeps blowing!


  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Mitsubishi PUHZ-P100VHA2-UK ACTM board keeps blowing!

    Hello Eliot

    Reading your post regarding not want to disconnect the compressor to test it makes me think that you may not be qualified?

    Surely, if you know how to check a compressor, you would have done it now and posted that the compressor is either 'OK' or is the cause of your PCB's blowing.

    If you think the compressor is faulty, why don't you test it?

  6. #6
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: Mitsubishi PUHZ-P100VHA2-UK ACTM board keeps blowing!

    Its not PCB blowing, its just Active Noise Filter with reactor. I dont know words how to tell what wrong.
    After ACTM power going to IPM.
    I think topic starter dont tell us something interesting, what he dont understand.

  7. #7
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: Mitsubishi PUHZ-P100VHA2-UK ACTM board keeps blowing!

    Test compressor windings, it can be short circuit between windings. As the power module can be damaged because of an overheat. HeatSink pure?

  8. #8
    Join Date
    Apr 2013
    Location
    England
    Posts
    4
    Rep Power
    0

    Re: Mitsubishi PUHZ-P100VHA2-UK ACTM board keeps blowing!

    Quote Originally Posted by frank View Post
    Hello Eliot

    Reading your post regarding not want to disconnect the compressor to test it makes me think that you may not be qualified?

    Surely, if you know how to check a compressor, you would have done it now and posted that the compressor is either 'OK' or is the cause of your PCB's blowing.

    If you think the compressor is faulty, why don't you test it?
    Frank are you taking the P*ss?! I've checked the windings of the compressor, 0.8 ohms across each winding actually.
    Last edited by frank; 15-04-2013 at 10:15 AM. Reason: Expletives removed

  9. #9
    Join Date
    Apr 2013
    Location
    England
    Posts
    4
    Rep Power
    0

    Re: Mitsubishi PUHZ-P100VHA2-UK ACTM board keeps blowing!

    What I mean is I'm worried about switching unit on again and blowing a third ACTM board, but yea agree with rusbuka, could be heat sink problem, not dispersing the heat therefore blowing the board!

  10. #10
    Join Date
    Oct 2009
    Location
    Sydney
    Age
    38
    Posts
    69
    Rep Power
    15

    Re: Mitsubishi PUHZ-P100VHA2-UK ACTM board keeps blowing!

    heat transfer paste?
    thats exactly what happens if heat paste is required and not fitted....
    can only take a few minutes..

  11. #11
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: Mitsubishi PUHZ-P100VHA2-UK ACTM board keeps blowing!

    If the winding becomes isolated on itself, its resistance will change a little, and here the quantity of rounds will exchange. That will lower the capacity and power keys will be heated more strongly. It is possible to check it only measurement of inductance of each winding.

  12. #12
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Mitsubishi PUHZ-P100VHA2-UK ACTM board keeps blowing!

    have u meggered it??
    Quote Originally Posted by Elliot View Post
    Frank are you taking the P*ss?! I've checked the windings of the compressor, 0.8 ohms across each winding actually.
    Last edited by frank; 15-04-2013 at 10:34 AM.

  13. #13
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Mitsubishi PUHZ-P100VHA2-UK ACTM board keeps blowing!

    Quote Originally Posted by install monkey View Post
    have u meggered it??
    Stop insulting the man! Jeez!
    Mostly found in Oxfordshire, UK :)

  14. #14
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Mitsubishi PUHZ-P100VHA2-UK ACTM board keeps blowing!

    valid question as the poster hasnt mentioned about testing the windings to earth
    QUOTE=monkey spanners;276794]Stop insulting the man! Jeez![/QUOTE]

  15. #15
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Mitsubishi PUHZ-P100VHA2-UK ACTM board keeps blowing!

    The only thing I can think of is the compressor is faulty but don't want to try it or disconnect it in case the board blows again


    Not what I would call an experienced method of testing

  16. #16
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Mitsubishi PUHZ-P100VHA2-UK ACTM board keeps blowing!

    Quote Originally Posted by Elliot View Post
    I've checked the windings of the compressor, 0.8 ohms across each winding actually.
    What is the reading to earth?