Results 1 to 7 of 7
  1. #1
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    35
    Posts
    623
    Rep Power
    17

    outdoor fan spin and stop in heating mode



    hi
    i have question about split unit heatpump
    why does the outdoor fan spin and stop in heating mode
    i know that it stop during defrost mode
    but why its spin and stop in normal mode
    i encounter this case in all heat pump
    when i searched about this state in internet
    and i found that this case happen to protect the indoor unit from damage caused by the hi temperature and pressure
    but one said that fan stop to allow more cold refrigerant to cool the compressor and prevent the overheating of the compressor
    so which opinion is correct
    thanks all



  2. #2
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: outdoor fan spin and stop in heating mode

    it is to reduce the heat load

    if the indoor coil sensor notices the indoor unit is not shedding the heat and ending up with a high discharge temp/pressure. By stopping the outdoor fan the duty drops off so the indoor unit can recover back to a normal temp/pressure to prevent potential compressor damage.

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: outdoor fan spin and stop in heating mode

    ...and I thought it was for head pressure control.... lol

  4. #4
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    35
    Posts
    623
    Rep Power
    17

    Re: outdoor fan spin and stop in heating mode

    Quote Originally Posted by r.bartlett View Post
    it is to reduce the heat load

    if the indoor coil sensor notices the indoor unit is not shedding the heat and ending up with a high discharge temp/pressure. By stopping the outdoor fan the duty drops off so the indoor unit can recover back to a normal temp/pressure to prevent potential compressor damage.
    so you mean it work and stop to protect both compressor and indoor unit from damage

  5. #5
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: outdoor fan spin and stop in heating mode

    Quote Originally Posted by frank View Post
    ...and I thought it was for head pressure control.... lol
    that's a what not a why answer - but you knew that :-)

  6. #6
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: outdoor fan spin and stop in heating mode

    Quote Originally Posted by kefah View Post
    so you mean it work and stop to protect both compressor and indoor unit from damage
    only compressor

  7. #7
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    35
    Posts
    623
    Rep Power
    17

    Re: outdoor fan spin and stop in heating mode

    Quote Originally Posted by r.bartlett View Post
    only compressor
    thank you man