    FUJITSU Inverter R410a not working, flashing lights



    Hi,

    My AC is not working. It had been working fine yesterday and this morning. It currently is not working and it flashing lights:

    Operation light: 10 flashes
    Timer light: 1 flash
    Economy light: continuous flashing


    I have pressed the reset button and has not worked. I have also checked the manual and have not found any solutions

    Any help would be much appreciated

    Thank you
    Brighter



  2. #2
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: FUJITSU Inverter R410a not working, flashing lights

    I need model name

  3. #3
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    35
    Posts
    624
    Rep Power
    16

    Re: FUJITSU Inverter R410a not working, flashing lights

    is the indoor unit or outdoor unit work

  4. #4
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,045
    Rep Power
    35

    Re: FUJITSU Inverter R410a not working, flashing lights

    From the fault code description with a flashing economy light (also green) then I guess this is a newer model with standardised fault codes. Model for outdoot would be AOTG... The G is the important part here to signify I am on the right track and the model is the newer generation.

    This code is discharge temperature error - meaning outdoor PCB has determined that discharge probe has gone over 110*C twice in 24hrs.

    Commonly caused by low refrigerant charge but there can be other causes.

    Of course a model number would confim my detective work here.

    Cheers,
    Sherlock Holms.
    Health and safety first..........unless I'm in a hurry.

  5. #5
    Join Date
    Apr 2013
    Location
    Australia
    Posts
    6
    Rep Power
    0

    Re: FUJITSU Inverter R410a not working, flashing lights

    Hi

    My apologies

    The model number is ASTG24LVCA

    The indoor unit turns on and flashes, no air flows through at all. The outdoor unit, the fan doesn't spin. (I thought this was because the indoor unit didn't work properly, but have no idea)

  6. #6
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: FUJITSU Inverter R410a not working, flashing lights

    Definitely need to take the advice of Tayters but then you need a serviceman.
    You can check cleanliness of outdoor heat exchanger at user level.

  7. #7
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: FUJITSU Inverter R410a not working, flashing lights

    If you turn the mains power to the whole system OFF for 10 minutes and then back ON again, will the system start?


  8. #8
    Join Date
    Apr 2013
    Location
    Australia
    Posts
    6
    Rep Power
    0

    Re: FUJITSU Inverter R410a not working, flashing lights

    Thank you everyone :-)

    I have no idea what this means:

    -----
    This code is discharge temperature error - meaning outdoor PCB has determined that discharge probe has gone over 110*C twice in 24hrs.

    Commonly caused by low refrigerant charge but there can be other causes.

    -----

    I did clean the filters and had it turned off for minutes after cleaning. It worked after I did this.

    However, yesterday I did switch the power on and off at the circuit board a number of times and did this not work. Why does the amount of time it is switched off matter?

    Thank you to everyone who replied, much appreciated

  9. #9
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: FUJITSU Inverter R410a not working, flashing lights

    The theory is that if the system hasn't got power for a couple of minutes, when the power returns the system will do a full reboot.
    So if it is a fault that requires a sensor to reach a preset temperature twice in 24 hrs, the system would start up and run for a short time. If the system doesn't start up at all it is likely to be another fault.


    If you are competent and confident to open up the outdoor unit you can check the temperature (using a good quality digital thermometer with suitable probe) of the compressor's discharge pipe as close to the compressor as possible, this is the smaller pipe connected to the compressor. When the system is running normally and for at least 15 minutes before you take the reading this should be below 100*C (normally you would expect it to be below 90*C).

    If you find that it is operating above 100*C you can tell your service technician that the system is most likely short of refrigerant and if it is running below 100*C ask him to bring a new discharge sensor.


  10. #10
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: FUJITSU Inverter R410a not working, flashing lights

    The Viking said that the power should be turned off for 10 minutes or more. it is necessary for full discharge of electrolytic capacitors into outdoor unit.
    And needed cleaning outdoor unit.

  11. #11
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: FUJITSU Inverter R410a not working, flashing lights

    It is good that it not J series of the equipment.

  12. #12
    Join Date
    Apr 2013
    Location
    Australia
    Posts
    6
    Rep Power
    0

    Re: FUJITSU Inverter R410a not working, flashing lights

    Ahh I see

    Unfortunately I can not get to the unit as the landlord has put it in a cage. I can see the unit etc just can not reach it.

    The air con is working fine after cleaning filters and switching off for 20 minutes. Would the service man still be able to pick up if there is a problem with the outdoor unit? (keeping in mind it has been working for 24 hours now)

  13. #13
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: FUJITSU Inverter R410a not working, flashing lights

    I assume that cage prevents air circulation
    and during maximum solar energy the outdoor unit have overheating.

  14. #14
    Join Date
    Apr 2013
    Location
    Australia
    Posts
    6
    Rep Power
    0

    Re: FUJITSU Inverter R410a not working, flashing lights

    the cage is just a metal cage to prevent people tampering with the unit, airflows through it --- like a heavy duty wire cage

  15. #15
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: FUJITSU Inverter R410a not working, flashing lights

    Do you can upload photos with installation of outdoor unit?

  16. #16
    Join Date
    Apr 2013
    Location
    Australia
    Posts
    6
    Rep Power
    0

    Re: FUJITSU Inverter R410a not working, flashing lights

    I can't, it's in a cage with some other units

  17. #17
    Join Date
    Jun 2008
    Location
    NZ
    Posts
    102
    Rep Power
    17

    Re: FUJITSU Inverter R410a not working, flashing lights

    I had this recently - a near new unit, used almost exclusively in cooling, would fault in warmer weather.

    All thermistors checked out ok, temps ok.

    The only solution available was to replace all electronics in the outdoor unit.

    No further faults so far - but then again, it hasn't exactly been warm since.

  18. #18
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: FUJITSU Inverter R410a not working, flashing lights

    2 brighter
    I dont need the focus on your unit I need a general view.

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •