    Update!

    Replaced compressor today and its now all working fine! Phew! I am so happy and relieved that it was the comp :-)
    I got an acid test kit but was unable to get any oil out of old comp to test it... Never done it before so not sure what the procedure is so any advice is welcome.
    Ran system in heating and got discharge up at 30 bar with nice 50 degrees air off indoor unit so client is over the moon, got 5 degrees air off in cooling too.
    Thanks for your help guys I would've struggled even more without your input!
    Kelly



  2. #52
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Compressor not pumping?

    Air off temps are meaningless without air on temps, we need to know the air on and air off temps for both coils in both modes... and compressors almost never die of natural causes.