    Frozen Evaporator Motors



    Went to our local ice-cream manufacturer today to check the cold stores, one at -27°C the other at -24°C.

    On the whole not too bad, they had lost a controller due to recent power fluctuations but soon fixed.

    The problem they have is with the evaporator fan motors freezing up during defrost, the bearings dry (frozen grease?) and the motors lock up.

    Does anyone have any knowledge of using heaters to protect the motors and also the fan blades from sticking to the fan cowl.


    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  2. #2
    Join Date
    Feb 2001
    Location
    USA
    Age
    63
    Posts
    264
    Rep Power
    24


    Can you tell us any more? You say the motor won't start, but also mention the fan blades are sticking to the cowl? How are the blades sticking... there should be no frost on the cowl.

    How often and for what length of time is there a defrost cycle?

    Do the defrost heaters completely clear the coil before returning to the cooling mode?

    This is ice cream... do they manufacture it or buy it and at what temperature does the ice cream come into the cold space?

    -24°C and -27°C is really not all that cold for ice cream... it works if the ice cream comes in "brick hard". I would be looking for a temperature of -29°C to -32°C. But again... receiving temperature may be a concern and not the holding temperature... just thinking. Most times I have seen fans freeze up on ice cream cabinets it was due to high latent heat load...
    :D
    Dean
    Subzero*psia

    Extinction is simply proof of failure to adapt.

  3. #3
    Join Date
    Apr 2001
    Location
    Southern England
    Age
    66
    Posts
    123
    Rep Power
    24

    Cool Could be....

    Last time I went though this the problem was traced to the condensate drain line (no effective P trap). Warm air ingress was frosting up the coils around the fan and placing huge load on them. The end result was a pile of bent fans and broken motors. Difficult to find as the evidence disappeared quickly.

    A typical customer to blame but never said sorry or paid for the pile of damaged parts ISTR.

    Who's evap is it?
    Derek

  4. #4
    Join Date
    Feb 2001
    Location
    USA
    Age
    63
    Posts
    264
    Rep Power
    24

    Smile Good thought Derek!

    Another problem is missing insulation or seal-gum around suction or liquid lines entering the cabinet. If the unit is a walkin, another common problem is worn door sweeps.
    :D
    Dean
    Subzero*psia

    Extinction is simply proof of failure to adapt.

  5. #5
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Unhappy

    Hi, welcome to the world of industrial refrig. Most cold stores suffer from the afore mentioned problem, it is due to moisture in the air sucked into the store by open doors. Usual icecream stores have propeller type high air flow fans fitted with pheriphial heating initiated during defrost and terminated after the drain down period. I am at the moment pricing a dehumidification and refrigeration project for a coldstore loading bay, the idea being to remove the moisture before it sticks to the evaporators. Also I may be wrong but you temperature see very low, with most stores I work in running at -25c return air, this low temperature will lead to even more moisture being sucked in. As for the grease unless they are very small fan motors the grease freezing will not be a factor.
    I spent 3 hours today just removing ice from cooler in a icecream store, the door had been broken and moiture had been sucked right through the evaporator building up in the area behind the fans tripping them out, so you are not on your own.
    Regards. Andy.

  6. #6
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    753
    Rep Power
    25
    I'm with Andy, sounds like door constantly open. As a short term fix you could extend dripping/drain time to allow droplets to clear off fans or as Andy suggested raise storage temp to approx -25C to reduce quantity of moisture sucked into room.

  7. #7
    Join Date
    Feb 2001
    Location
    USA
    Age
    63
    Posts
    264
    Rep Power
    24

    Smile What about it Brian....

    Have you solved the problem yet? Do tell us as we have a several possible solutions posted on here and we are all waiting to see how you solved it.


    :D
    Dean
    Subzero*psia

    Extinction is simply proof of failure to adapt.

  8. #8
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60
    Sorry Dean, no I haven't solved this one yet but the suggestions all hold good.

    The main door seal wasn't making because the door slides had come loose

    They do have a drainage problem aswell....there are two ice mountains below one of the evaporators which the guy tends to clear out by driving his fork-lift truck at them

    Also they lost one or the compressors a few days ago which I think was due to an oil separator problem along with old age.

    They keep promising to shut down the cold store for maintenance, firstly Oct the Feb then Oh I don't know. These ex-farmers are a breed on their own !
    Last edited by Brian_UK; 06-11-2001 at 10:33 PM.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  9. #9
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24
    Hi, Brian, having fun? Loads of coldstores seem to be owned by ex-farmers, I can think of one or two and yes they are mostly a law unto themselves. With regards to emptying the colstore for maintenance, we don't the customers just don't like it, anyway most of the stores I work in have anything from 5000 ton up product in them, it would not be possible to empty them. We work away with suits on (deep freeze) mostly our coolers are de-iced, after clearing the drains by hot wash power washers with the nozzle removed. As for access we us either platforms or reach trucks with safety cages.
    It's all hard work and none too warm, but mostly the stores I work in are under contract, so you make certain the ice does not build as it is you clearing it. As for freeze ups due to door, seen by the snow trail, we charge for them, it soon teaches the client to keep the door shut and in working order.
    Regards. Andy.

  10. #10
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60
    Originally posted by Andy
    Hi, Brian, having fun?
    Yes and no Andy...

    I can't think exactly what our service period is off hand; it's either twice or three times a year so keeping a decent track of what's happening is difficult.

    Going back some months when the client was at the Goodwood Festival of Speed we had several overnight callouts because his -27°C coldstore wasn't holding temperature.

    Go inside - one evap with 3 fans running, the other with only 1 fan running; both evaps fed from the same compressor (R404a).

    All sorts of fun spent there ! Ended up on Sunday night stripping out one fan from the good unit to put in the other one along with defrosting, de-icing fans and motors - oh the list goes on....

    Clients comment - Oh yeah, we've only had one fan running for a while. Kept meaning to get it fixed etc etc

    Jeez, just the sort of thing you need isn't it ? I know we all get and it keeps coming in buckets full
    Last edited by Brian_UK; 06-11-2001 at 10:34 PM.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  11. #11
    Join Date
    Jan 2002
    Location
    Austin, Texas
    Posts
    716
    Rep Power
    23
    The EVAPS wouldn't happen to be Russell brand, would they?

    I had constant bearing failure on Russell OEM motors. The box said "permanently sealed bearings". But when I took a bad bearing to the bearing store, Mr. Bearing told me tht the bearins in the motor were "shielded", not "sealed.

  12. #12
    Join Date
    Mar 2002
    Location
    west midlands
    Posts
    10
    Rep Power
    0

    Smile

    hi brian,
    ive spent many an afternoon clearing ice from stuck evap fans,doesnt your blowers have periheral heaters on them to help prevent edge of blade sticking to cowling an then triping out fan motors?extending drain down i find makes matters worse due to residual heat/steam rising and adhering to cold surfaces ,cowling,tips of blades etc from defrost heaters even when terminated after DEF.

  13. #13
    Join Date
    Apr 2002
    Location
    Manchester UK city of rain
    Age
    51
    Posts
    37
    Rep Power
    0
    Used to get the problem of ice holding fan onto fan blades a lot with a certain large frozen food chains coldstores, trouble was the KS range of searle evaps produce steam when defrosting due to only having two defrost heaters which therefore have to get very hot. Actually got Searle to recognise the problem and they supplied peripheral heaters to be retrofitted to the blowers.

    (Still don't fit them as standard though)

    Simon.

    p.s. something we tried before getting the heaters was smearing the cowlings with vaseline or grease to make the water bead and stop it sticking!

  14. #14
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60
    Thanks Simon.

    Yes they were Searle but the problem is no longer mine now as I have left that firm and area.

    I must admit that I like the sound of the vaseline though, simple but effective - always the best !
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  15. #15
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25
    Brian. I enjoy all your posts, but you have a signature that states that you you are presently not employed. Do you also have a business card that says the same?

  16. #16
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60
    LOL Dan.

    Yes, now that my house move is over I am now having to seriously look for work again but I think I will pass on the business card idea.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

Similar Threads

  1. Nite shades causing frozen product
    By kengineering in forum Commercial
    Replies: 27
    Last Post: 11-04-2006, 12:59 AM
  2. Freezing tunnels vs frozen products store
    By jaxie072 in forum Technical Discussions
    Replies: 6
    Last Post: 08-03-2006, 02:51 AM
  3. Frozen Coils
    By subzero*psia in forum Commercial
    Replies: 0
    Last Post: 25-10-2001, 02:08 AM
  4. Frozen in the wrong place
    By Brian_UK in forum Chit Chat & Service Stories
    Replies: 0
    Last Post: 09-03-2001, 12:03 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •