    Question Re charge procedure is it correct?



    Hi
    Just put a Mitsubishi SRK50ZIX-S and had no gas in it( 2nd hand) and now it turns on but the inside fan is running but the shutters are closed and outside compressor not running?
    Can u check my method please as below.

    Evac for two hours down to 250microns
    Fit gas and purge at gauges to get rid of air and invert
    Both valves still open(should i have closed one?)
    Unit not running at this stage
    Fill with 1.4kg of gas but only took 1.1kg
    let settle for a few minutes
    Turn on to cooling and run
    turn off( think i should have left it running?)
    let 300g gas in
    Disconnect gauges
    Unit wont run

    Have i done this correctly, have i #@$%^ it?

    Hope you can shed some light on it or a least verify my procedure?
    Cheers



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Re charge procedure is it correct?

    3 minute delay on start up of outdoor unit, did u put the indoor cover on properly - u can prise the louvres into an open position - mitsi dont have a limit switch on the louvres- u can unplug the louvre on the indoor pcb.

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Re charge procedure is it correct?

    http://www.mediafire.com/view/?enugolbss5lfge4
    similar uk version - service manual

  4. #4
    Join Date
    Apr 2013
    Location
    New Zealand
    Posts
    4
    Rep Power
    0

    Re: Re charge procedure is it correct?

    The problem is not just that the louvres dont open its more that the thing dont start up ie the outdoor fan is not turning?

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Re charge procedure is it correct?

    outdoor fan will start up about 20 seconds before the compressor starts- check ur connections on the interconnecting.

  6. #6
    Join Date
    Apr 2013
    Location
    New Zealand
    Posts
    4
    Rep Power
    0

    Re: Re charge procedure is it correct?

    OK will do and thanks for the link but does my charging procedure look sound to you?
    I have another one to fully re charge and was wondering if i had caused damage somehow by the way i charged it?

  7. #7
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Re charge procedure is it correct?

    page 32 of the manual shows a flow chart, best to give it a long vac if the service valves were left open.
    your method is ok except for prior to vaccing - pressure test with oxygen free nitrogen to upto 40 bar- if r410a to proove all is ok before vaccing

  8. #8
    Join Date
    Apr 2013
    Location
    New Zealand
    Posts
    4
    Rep Power
    0

    Re: Re charge procedure is it correct?

    Hi
    FYI the problem was i did not have the original remote i bought a universal remote that appeared to work (made all the beeps etc) but in fact didnt. Found a remote and away it went!
    Thanks for your suggestions

  9. #9
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    35
    Posts
    624
    Rep Power
    16

    Re: Re charge procedure is it correct?

    Quote Originally Posted by install monkey View Post
    pressure test with oxygen free nitrogen to upto 40 bar- if r410a to proove all is ok before vaccing
    are you sure that he must pressure test to 40 bar or 4 bar

  10. #10
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,120
    Rep Power
    25

    Re: Re charge procedure is it correct?

    Quote Originally Posted by kefah View Post
    are you sure that he must pressure test to 40 bar or 4 bar
    Fookin 4bar !!!!!!! are you kidding me??
    40-43 bar depending on manufacturers specs
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  11. #11
    Join Date
    Jan 2011
    Location
    england
    Posts
    57
    Rep Power
    15

    Re: Re charge procedure is it correct?

    Was just about to say you sure you have the correct remote! Honest! Lol

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments