Just put a Mitsubishi SRK50ZIX-S and had no gas in it( 2nd hand) and now it turns on but the inside fan is running but the shutters are closed and outside compressor not running?
Can u check my method please as below.

Evac for two hours down to 250microns
Fit gas and purge at gauges to get rid of air and invert
Both valves still open(should i have closed one?)
Unit not running at this stage
Fill with 1.4kg of gas but only took 1.1kg
let settle for a few minutes
Turn on to cooling and run
turn off( think i should have left it running?)
let 300g gas in
Disconnect gauges
Unit wont run

Have i done this correctly, have i #@$%^ it?

Hope you can shed some light on it or a least verify my procedure?