    134A reach in cooler problem



    Newer cheap 2 door worked fine 3 yrs, now too warm;dirty condenser-blew out;sealed system, hermetic compressor, no access valves, cap tube; searched-no leaks; compressor hot, discharge line hot, evap cold but not enough; no noticeable temp change along cap tube, no icing; I suspect partly plugged cap or oil return problem (condenser below). Tomorrow I will go back with tap in valve and recover, blow out cap tube,pressure test, change dryer; recharge.
    134A is a pain.



  2. #2
    Join Date
    Oct 2005
    Location
    In a 2 bedroom unit. Why's That? :)
    Posts
    314
    Rep Power
    19

    Re: 134A reach in cooler problem

    did you check the thermostat? Is it positioned correcty and is it switching at the right temp?

  3. #3
    Join Date
    Dec 2005
    Location
    usa
    Posts
    5
    Rep Power
    0

    Re: 134A reach in cooler problem

    Thermostat is at cold limit, and I can hear it click..box running at 53 degrees. Stat looks ok.

  4. #4
    jpz06's Avatar
    jpz06 Guest

    Re: 134A reach in cooler problem

    Hi, This is my first post so there may already be an answer to this. I have been dealing with this problem for a while on new 134 a systems (cap. tube) the problem is with the poe oil that is in the compressors. what I do when I have a plugged cap tube (134-a) is replace cap tube , blow out lines, replace filter dryer, and very important change oil in compressor, some how the oil in the compressor breaks down when the compressor overheats (plugged condenser ) if you break open the cap tube can see like scale forming inside.

  5. #5
    william_wye's Avatar
    william_wye Guest

    Re: 134A reach in cooler problem

    we have had similar and numerous problems with reach in coolers, where cap blocks up...... The problem is with the POE oil.....How to prevent this from happening??? Someone said keep unit well maintained..(clean and clear condensor coils)..tried that ..to no avail.....Anyone got better solutions?

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: 134A reach in cooler problem

    Quote Originally Posted by william_wye View Post
    we have had similar and numerous problems with reach in coolers, where cap blocks up...... The problem is with the POE oil.....How to prevent this from happening??? Someone said keep unit well maintained..(clean and clear condensor coils)..tried that ..to no avail.....Anyone got better solutions?
    Maybe to change capillary with other of bigger bore and longer.

  7. #7
    Join Date
    Jan 2009
    Location
    Queensland
    Age
    64
    Posts
    113
    Rep Power
    16

    Re: 134A reach in cooler problem

    Hi bvis, does the compressor have a run capacitor?
    A crook run cap will cause your compressor to run hot and possibly cycle on its overload, causing the case to run warm.
    It should be within 10% of the capacitance marked on the cap.
    If you do have to replace it, you can use a cap of greater voltage rating, but not less.
    Just a thought.

    Edit: by the way, even if the capillary is restricted, it could still be caused by a faulty run cap causing the compressor to run hot and cooking the oil.
    Or it may just be that dirty condenser.
    Last edited by Slatts; 07-03-2009 at 09:44 AM.

  8. #8
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: 134A reach in cooler problem

    I see no reason to suspect the cap tube.

    For that matter we haven't been given enough information to suspect anything.

  9. #9
    Join Date
    Mar 2009
    Location
    idaho
    Age
    45
    Posts
    8
    Rep Power
    0

    Re: 134A reach in cooler problem

    Quote Originally Posted by bvis View Post
    Newer cheap 2 door worked fine 3 yrs, now too warm;dirty condenser-blew out;sealed system, hermetic compressor, no access valves, cap tube; searched-no leaks; compressor hot, discharge line hot, evap cold but not enough; no noticeable temp change along cap tube, no icing; I suspect partly plugged cap or oil return problem (condenser below). Tomorrow I will go back with tap in valve and recover, blow out cap tube,pressure test, change dryer; recharge.
    134A is a pain.
    on 134a the oil breakes down if the condensor gets dirty,plugs the dryer and cap tubes, you realy have to keep the condensor clean poe oil just isnt very good.

  10. #10
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: 134A reach in cooler problem

    Also, OP Bvis hasn't come back since January 2006 - I think perhaps we are wasting our answers here....
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  11. #11
    ticotech's Avatar
    ticotech Guest

    Re: 134A reach in cooler problem

    get some piercing valve and check pressure, so we can have more info

  12. #12
    Join Date
    Jan 2009
    Location
    Queensland
    Age
    64
    Posts
    113
    Rep Power
    16

    Re: 134A reach in cooler problem

    Quote Originally Posted by Brian_UK View Post
    Also, OP Bvis hasn't come back since January 2006 - I think perhaps we are wasting our answers here....
    Well....
    That was kind of embarrassing.

Similar Threads

  1. York Screw Oil Problem
    By tomt in forum Technical Discussions
    Replies: 10
    Last Post: 02-12-2009, 02:48 PM
  2. Strange problem
    By Peter_1 in forum Electrical
    Replies: 9
    Last Post: 10-04-2007, 05:19 PM
  3. hello i've got problem with charging
    By def-j in forum Fundamentals
    Replies: 3
    Last Post: 21-06-2006, 08:57 PM
  4. Problem with centrif - help requested
    By Brian_UK in forum Industrial Compressors