    Angry Aermec air to water heat pump



    Hi has anybody ever had any trouble with a aermec unit that seems to go on defrost very often (d1) I have also found the unit cuts off on fault h1 and it has to be manually reset. I have looked through the net but can't seem to get any info on the controller for fault codes the controller is called u chiller. i would really appreciate any help , cheers



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Aermec air to water heat pump

    Never worked on Aermec myself but,

    Excessive defrosts could be a dirty outdoor coil, obstructed airways around the outdoor unit or a lack of refrigerant.



    .

  3. #3
    Join Date
    Jan 2009
    Location
    Ireland
    Age
    42
    Posts
    34
    Rep Power
    0

    Re: Aermec air to water heat pump

    Thanks for the reply I checked every thing like that and all is good I'd like to get into parameters to check probs etc but I am having trouble finding a manual. I will email aermec tonight to see if they can help , cheers

  4. #4
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Aermec air to water heat pump

    Ring Design Air Limited in Dublin they are the agents .
    U chiller controller is more than likely a Carel micro chiller controller
    http://www.carel.com/carelcom/web/en...id_prodotto=17
    Cheers
    Stu
    Last edited by stufus; 02-04-2013 at 10:54 PM. Reason: link
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!