    Site Glass Flashing



    I ran across a meat case today that i noticed the site glass would be full and no bubbles for a while and then liquid would disappear for 2 or 3 minutes and start back flowing. The owner said he has never had problems with it. The reciever liquid level is right at 80 percent full. So i dont think it is low on charge.. I have not put gauges on it, because he said he has never had a problem with it.
    My question is this......What are some things that would cause the site glass to do that?
    Will it harm the unit ? What do i look for to find out whats causing it and to fix it ?



  2. #2
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    52
    Posts
    1,083
    Rep Power
    23

    Re: Site Glass Flashing

    Hi jakb
    Have you searched the search function on this forum - the sightglass has been done recently, check it out.

  3. #3
    Join Date
    Jun 2010
    Location
    USA
    Posts
    89
    Rep Power
    14

    Re: Site Glass Flashing

    Quote Originally Posted by Tesla View Post
    Hi jakb
    Have you searched the search function on this forum - the sightglass has been done recently, check it out.
    I did but didn't see what I was looking for.... can you send a link to it ? I checked SC and it is 7 degrees and SH is 31 degrees..... the evaporator SH is 4 degrees which tells me its flooding the evaporator....... would that cause what I am seeing at the site glass ? Its 404A ***** if it matters

  4. #4
    Join Date
    Sep 2011
    Location
    USA
    Age
    45
    Posts
    84
    Rep Power
    14

    Re: Site Glass Flashing

    It is possible that the pressure in the receiver gets too low.

  5. #5
    Join Date
    Jun 2010
    Location
    USA
    Posts
    89
    Rep Power
    14

    Re: Site Glass Flashing

    Quote Originally Posted by Coorsman777 View Post
    It is possible that the pressure in the receiver gets too low.
    What would cause that ? And how do you fix it ? I did notice it has a 5/8 liquid line and total run on line set is probably 80 feet and its pulling 3 different cases

  6. #6
    Join Date
    Jan 2008
    Location
    north west
    Age
    42
    Posts
    234
    Rep Power
    19

    Re: Site Glass Flashing

    Is it possible that all the systems are calling for cooling at the same time?

  7. #7
    Join Date
    Jun 2010
    Location
    USA
    Posts
    89
    Rep Power
    14

    Re: Site Glass Flashing

    Quote Originally Posted by 1mikeefc1 View Post
    Is it possible that all the systems are calling for cooling at the same time?
    Yes...all are hooked to the same unit . Would that cause it ? And why ?

  8. #8
    Join Date
    Jan 2008
    Location
    north west
    Age
    42
    Posts
    234
    Rep Power
    19

    Re: Site Glass Flashing

    Well in theory I suppose it shouldn't but if all the cabinets are calling for refrigeration at the same time it could cause the sight glass to look empty but as they satisfy at different times the level could alter according to how much is needed. Not 100 percent just throwing an idea out there.

  9. #9
    Join Date
    Sep 2011
    Location
    USA
    Age
    45
    Posts
    84
    Rep Power
    14

    Re: Site Glass Flashing

    Was thinking this was on a rack system. Sometime if the receiver pressurization is not set right liquid will not get pushed out of the receiver but rather almost pulled out to the txv's.