29-03-2013, 03:38 PM #1
Vacuum testing
I have a large 2k ton york chiller and made a couple leak repairs yesterday. After pulling the system into a deep vacuum to test for leaks I got these numbers. 1.116 microns after vac complete. with oil heater still on and 1 hour later my vac was 1.516, an increse of 400 microns. Does this seem normal or do I still have a significant leak?
-
29-03-2013, 06:56 PM #2
Re: Vacuum testing
keep monitering it- ur initial increase is normal, if it still increases then keep vaccing- could just be refrigerant migrating out the oil.
after all you did pressure test it and all was ok
-
30-03-2013, 06:57 AM #3
Re: Vacuum testing
you might have moisture in the system
-
30-03-2013, 12:32 PM #4
Re: Vacuum testing
Is that a 2000ton chiller? Just a guess but is it possible on something that size it may take a while for the vacuum level to even out, depends where your vac gauge is etc
Mostly found in Oxfordshire, UK :)
-
30-03-2013, 01:31 PM #5
Re: Vacuum testing
Surely a pressure test would have brought a leak to your attention not the evacuation?
-
30-03-2013, 09:59 PM #6
Re: Vacuum testing
I am confused with your numbering system, sorry it's a UK thing...
You say you have a micron reading of 1.116 which to me is 1 decimal 116 microns or are you saying that you have a reading of 1 thousand 1 hundred and 16 micron? If it is the one thousand plus reading then it is not a deep vacuum yet.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
31-03-2013, 07:11 PM #7
Re: Vacuum testing
What type of chiller? YK/YS or air cooled, if one of the first two you may never attain deep vacuum given that there is a shaftseal present, if air cooled you need better numbers but keeping the oil warm will help.
alecMostly found in the southern part of this green and pleasant land.