    Vacuum testing



    I have a large 2k ton york chiller and made a couple leak repairs yesterday. After pulling the system into a deep vacuum to test for leaks I got these numbers. 1.116 microns after vac complete. with oil heater still on and 1 hour later my vac was 1.516, an increse of 400 microns. Does this seem normal or do I still have a significant leak?



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Vacuum testing

    keep monitering it- ur initial increase is normal, if it still increases then keep vaccing- could just be refrigerant migrating out the oil.
    after all you did pressure test it and all was ok

  3. #3
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: Vacuum testing

    you might have moisture in the system

  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Vacuum testing

    Is that a 2000ton chiller? Just a guess but is it possible on something that size it may take a while for the vacuum level to even out, depends where your vac gauge is etc
    Mostly found in Oxfordshire, UK :)

  5. #5
    Join Date
    Jan 2008
    Location
    north west
    Age
    42
    Posts
    234
    Rep Power
    19

    Re: Vacuum testing

    Surely a pressure test would have brought a leak to your attention not the evacuation?

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Vacuum testing

    I am confused with your numbering system, sorry it's a UK thing...

    You say you have a micron reading of 1.116 which to me is 1 decimal 116 microns or are you saying that you have a reading of 1 thousand 1 hundred and 16 micron? If it is the one thousand plus reading then it is not a deep vacuum yet.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Vacuum testing

    What type of chiller? YK/YS or air cooled, if one of the first two you may never attain deep vacuum given that there is a shaftseal present, if air cooled you need better numbers but keeping the oil warm will help.

    alec