    What are my options ?



    For cooling air at standard max uk ambients to -30 degrees C

    Air flow required is 60000 litres per minute delivered at -30deg C no less

    Cooling of the air is required for 1 hour

    Thats all the info i have at present

    What options would you gents suggest ?



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: What are my options ?

    i suggest-get a consultant to spec it

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: What are my options ?

    With a delta t of 57k I would suggest that you do it in stages as you need high temp, medium temp and low temp systems to achieve the end result

  4. #4
    Join Date
    Aug 2006
    Location
    UK
    Age
    57
    Posts
    11
    Rep Power
    0

    Re: What are my options ?

    Quote Originally Posted by frank View Post
    With a delta t of 57k I would suggest that you do it in stages as you need high temp, medium temp and low temp systems to achieve the end result
    Thanks

    Nice idea, hadnt thought of that

    What sort of kW would i be looking at for this ?

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: What are my options ?

    Do you know how to design such systems?

  6. #6
    Join Date
    Aug 2006
    Location
    UK
    Age
    57
    Posts
    11
    Rep Power
    0

    Re: What are my options ?

    Quote Originally Posted by frank View Post
    Do you know how to design such systems?
    Im just a little rusty as its been a long time since i did any calcs like this.

    Did an Apprenticship in mechanical and electrical, served my mechancial time working and installing Grasso RC611 LPR systems on spiral blast freezers, did some really nice frick screws and also the general run of the mill small recip's like bitzer and prestcold.

    Also did some (in their infancy) rotocold rotarys which were also sold by frick in the frick days.

    Fitted some of the first danfoss electronic TEV's with the fridge plant running on Toshiba Inverters (again some of the first Inverters in the UK for that).

    Used to design systems but we are talking - a long time ago - early rotocold days (anyone care to guess the rough age of those days? )

    I moved out of that field and now do a lot of large electrical contracts, renewable energy, solar, control panels, BMS, Inverters (AC and DC), PLC's, Devicenet, Profibus, Can etc all in the range of 22-1000kW.

    Have got a very good friend who's a designer with his own consultancy business (HVAC and low temp stuff) but he's on holiday, so i thought i would pop by here and see what ideas the forum could muster up and advice i could get to give me a head start.

    So there you go.....

  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: What are my options ?

    LOL.....quite a lot of detail in such a short life (46 years old??)..

    No offence, but we get quite a lot of numpties on here asking similar questions, and when they get the answer, they don't understand it and we don't seem to hear from them again.

    Anyway, 60,000 litres/minute equates to 1m3/s, so not a great amount of airflow.

    To bring 1m3/sec down from +27C to -30C requires 98.61kW of heat rejection.

    You can split this into 3 stages of cooling , high (+27 to +10) 29.41kW, medium (+10 to -10) 34.6kW and low (-10 to -30) 34.6kW and select your equipment to suit.

    I would think that you may have issues with defrost though impacting on your -30C requirement for 1 hour.
    Last edited by frank; 31-03-2013 at 07:13 PM.

  8. #8
    Join Date
    Aug 2006
    Location
    UK
    Age
    57
    Posts
    11
    Rep Power
    0

    Re: What are my options ?

    Quote Originally Posted by frank View Post
    LOL.....quite a lot of detail in such a short life (46 years old??)..

    No offence, but we get quite a lot of numpties on here asking similar questions, and when they get the answer, they don't understand it and we don't seem to hear from them again.

    Anyway, 60,000 litres/minute equates to 1m3/s, so not a great amount of airflow.

    To bring 1m3/sec down from +27C to -30C requires 98.61kW of heat rejection.

    You can split this into 3 stages of cooling , high (+27 to +10) 29.41kW, medium (+10 to -10) 34.6kW and low (-10 to -30) 34.6kW and select your equipment to suit.

    I would think that you may have issues with defrost though impacting on your -30C requirement for 1 hour.
    46 - But i started at 15 so a few years behind me

    Thanks for the reply

  9. #9
    Join Date
    Aug 2006
    Location
    UK
    Age
    57
    Posts
    11
    Rep Power
    0

    Re: What are my options ?

    I see what your saying about 3 stages of cooling.

    Are we talking of 3 seperate systems here or 3 evaps ?

    I was thinking of a two stage screw set up....

    Now as i have been out of play for a lot of years, the makes i sued to have a lt to do with were

    Grasso, Frick, J&E Hall and Sabroe

    All still in business but albeit changed or new owners etc etc

    Any comments on the above manufacturers or any others ?

    We did an inverter repair on a 160kW Italian package unt the other day, screw semi - frascold - it has to be one of the cheapest worst piece of engineering i have ever seen, total garbage and it wasnt cheap.....

    (Screw blew up after 14 months, the inverter on the second system blew up after 16 months (twin system)) - customer not a happy chappy.....

  10. #10
    Join Date
    Aug 2006
    Location
    UK
    Age
    57
    Posts
    11
    Rep Power
    0

    Re: What are my options ?

    Nothing ? No Replies ?

  11. #11
    Join Date
    Aug 2006
    Location
    UK
    Age
    57
    Posts
    11
    Rep Power
    0

    Re: What are my options ?

    Quote Originally Posted by install monkey View Post
    i suggest-get a consultant to spec it
    Thats really for another debate / thread

    In my opinion there are good consultants and there are bad consultants, in a lot of the industries i work in i have come across a lot of bad ones compared to not so many good ones.

  12. #12
    Join Date
    Jul 2013
    Location
    U.S.A
    Age
    33
    Posts
    8
    Rep Power
    0

    Re: What are my options ?

    In my opinion get a consultant!!!!!!!!!!!
    In a lot of the industries i am work and i have come across a lot of bad ones compared to not so many good ones.

  13. #13
    Join Date
    Jul 2013
    Location
    U.S.A
    Age
    33
    Posts
    8
    Rep Power
    0

    Re: What are my options ?

    Quote Originally Posted by welray View Post
    In my opinion get a consultant!!!!!!!!!!!
    In a lot of the industries i am work and i have come across a lot of bad ones compared to not so many good ones.
    Do you like!!
    Last edited by frank; 29-07-2013 at 01:33 PM.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •