    Condensing pressure regulator with thermosyphon oil cooling



    Dear All!
    Because of low condensing pressure in ammonia plant in winter time (it is difficult to do hot gas defrosting) I need condensing pressure regulator ICS + CVP and ICS + CVPP (HP) on discharge pipe.
    But I have thermosyphon oil cooling with pilot receiver connected with high pressure receiver and condenser by equalizer line. And it is impossible to use check valve on drain line to high pressure receiver (it needs dP to open). What I have to do? Please help.



  2. #2
    Join Date
    Mar 2013
    Location
    Korea
    Posts
    10
    Rep Power
    0

    Re: Condensing pressure regulator with thermosyphon oil cooling

    I understand by myself, to formulate a question is to answer then half. We need only pressure regulator ICS + CVP, no check valves, because we need high discharge pressure only for hot gas defrosting.

  3. #3
    Join Date
    Jun 2011
    Location
    Australia
    Age
    44
    Posts
    336
    Rep Power
    21

    Re: Condensing pressure regulator with thermosyphon oil cooling

    Wouldn't it be easier to just cycle off the condenser fans?

  4. #4
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Condensing pressure regulator with thermosyphon oil cooling

    Good point H.

    Simple solutions are always the ones to try first.
    I think they call it Oakums Razor or something similar?
    Grizzly

  5. #5
    Join Date
    Mar 2013
    Location
    Korea
    Posts
    10
    Rep Power
    0

    Re: Condensing pressure regulator with thermosyphon oil cooling

    ambient temperature maybe -30 C and windy

  6. #6
    Join Date
    Jun 2011
    Location
    Australia
    Age
    44
    Posts
    336
    Rep Power
    21

    Re: Condensing pressure regulator with thermosyphon oil cooling

    Can you tell us more about the condensers. How many? Water cooled? Air Cooled? VSD Fans? Are all the fans off & still low condensing?

    How long during the year is this a problem?

  7. #7
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Condensing pressure regulator with thermosyphon oil cooling

    Quote Originally Posted by Andrew5447 View Post
    ambient temperature maybe -30 C and windy
    You can isolate one condenser or install shield to prevent direct wind. What pressure do you need for the defrosting?

  8. #8
    Join Date
    Mar 2013
    Location
    Korea
    Posts
    10
    Rep Power
    0

    Re: Condensing pressure regulator with thermosyphon oil cooling

    Quote Originally Posted by HVACRsaurus View Post
    Can you tell us more about the condensers. How many? Water cooled? Air cooled? VSD Fans? Are all the fans off & still low condensing?

    How long during the year is this a problem?
    We have 2 air cooled condensers with 8 fans each. No VSD for Fans. All the fans off during low condensing of course. There are severe winters 3-4 month per year.

  9. #9
    Join Date
    Mar 2013
    Location
    Korea
    Posts
    10
    Rep Power
    0

    Re: Condensing pressure regulator with thermosyphon oil cooling

    In winter compressor's load falls down as heat leakage drop (it is cold storage). We did not have enough hot gas for defrosting, the condensing pressure falls especially at low ambient temperature. We need of condensing pressure at least 7-9 bar, not less I think.

  10. #10
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Condensing pressure regulator with thermosyphon oil cooling

    Andrew, can you just consider what you posted earlier. Install PM with high pressure pilot valve or similar with hot gas connection taken off before it at your pre-set pressure 9 bar. Downstream is condenser with t/syphon return, equalizing line etc. In summer or warmer weather jut manually jack it open. Unless I'm missing something it could work. You may have to watch refrigerant level are adequate at this time, as well as enough load to generate hot gas.

  11. #11
    Join Date
    Jun 2011
    Location
    Australia
    Age
    44
    Posts
    336
    Rep Power
    21

    Re: Condensing pressure regulator with thermosyphon oil cooling

    Ok, I'm beginning to understand.

    At times the ambient is colder than the Coldstore! I suspect that the evaporators would likely be cycled off on temperature setpoint for extended duration...

    Hopefully this requires less frequent defrosting?

    I am wondering if valving off one condenser would help?

    Keep in mind - evaporator load is required to create hot gas. Each evaporator defrosting requires at least two similar evaporators running to create the hot gas. Are you able to set a low setpoint (say -40°C) for the purposes of maintaining evaporator load? Likely a similarly modified suction pressure setpoint would also be required..

  12. #12
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Condensing pressure regulator with thermosyphon oil cooling

    Quote Originally Posted by Andrew5447 View Post
    In winter compressor's load falls down as heat leakage drop (it is cold storage). We did not have enough hot gas for defrosting, the condensing pressure falls especially at low ambient temperature. We need of condensing pressure at least 7-9 bar, not less I think.
    Isolate one condenser.

  13. #13
    Join Date
    Mar 2013
    Location
    Korea
    Posts
    10
    Rep Power
    0

    Re: Condensing pressure regulator with thermosyphon oil cooling

    Quote Originally Posted by HVACRsaurus View Post
    Ok, I'm beginning to understand.

    At times the ambient is colder than the Coldstore! I suspect that the evaporators would likely be cycled off on temperature setpoint for extended duration... Yes!

    Hopefully this requires less frequent defrosting? Yes, but they need

    I am wondering if valving off one condenser would help? It is possible

    Keep in mind - evaporator load is required to create hot gas. Each evaporator defrosting requires at least two similar evaporators running to create the hot gas. Yes, because of this we do not have enough hot gas for defrosting - compressor's load falls down.
    Are you able to set a low setpoint (say -40°C) for the purposes of maintaining evaporator load? Likely a similarly modified suction pressure setpoint would also be required..
    yes it is possible, but it is not the best solution

    Thank you HVACRsaurus you are understanding!

  14. #14
    Join Date
    Mar 2013
    Location
    Korea
    Posts
    10
    Rep Power
    0

    Re: Condensing pressure regulator with thermosyphon oil cooling

    Thanks, Ranger 1, I think you are right. If we stop equalizing line, the high pressure receiver will be on pressure that is higher then in condensers lines and the pilot receiver, they will be overfilled by liquid. The working area of flooded condenser go down and at some I see liquid can drain to high pressure receiver. I hope it will be without hammering.
    The question is how to combine condensing pressure regulator and thermosyphon oil cooling.

  15. #15
    Join Date
    Feb 2013
    Location
    Rochester, NY
    Posts
    37
    Rep Power
    0

    Re: Condensing pressure regulator with thermosyphon oil cooling

    I have an A4AB valve in the discharge line up to the older condensers. Back before we expanded the plant it served to keep 130 psi of hot gas in the plant for defrosting purposes and would let any excess go to the roof. The first step in the condenser control sequence was to power that valve, opening it wide.

    Once we expanded I had liquid injection to deal with and couldn't let the pressure on the roof drop off so I started isolating condensers in the Winter. 2 of my 3 condensers are isolated now with outside temperature running about 7C. I don't have to worry about an equalizing line since my main receiver is controlled-pressure. I run it about 80 psi which low enough to get good liquid flow down from the condensers to the receiver and high enough to deliver liquid to the pump package and the intermediate loads. My pilot receiver, being upstream of the float-controlled condenser outlet valve, stays at full head pressure and I keep a decent flow of liquid to the LIC on the screws.
    Iceman717

    ---
    Compressors in the basement, condensers on the roof, evaporators everywhere else. :cool:

  16. #16
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Condensing pressure regulator with thermosyphon oil cooling

    Do you really need defrosting if -30C outside? What is the suction temperature? If your suction temperature is -30-35C, you don't need defrosting.
    If you really need defrosting, it should be done once per week or every second week, because rate of frost formation will be very slow. Lower set point for the freezers, run additional evaporators, run additional compressor and defrost.

  17. #17
    Join Date
    Nov 2009
    Location
    france
    Age
    64
    Posts
    225
    Rep Power
    19

    Re: Condensing pressure regulator with thermosyphon oil cooling

    IMG.pdf

    better than an explanation, a drawing

    try this, you need a check valve, 2 ICS/CVP. The ICS valve fitted to the hot gas line is designed to prevent too low discharge pressure at the compressors.
    the liquid to oil coolers must be connected at the bottom of liquid receiver and the liquid line to LP vessels higher.
    fans controlers have to be downstream of the check valve.

    regards

  18. #18
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Condensing pressure regulator with thermosyphon oil cooling

    Quote Originally Posted by cricri View Post
    IMG.pdf

    better than an explanation, a drawing

    try this, you need a check valve, 2 ICS/CVP. The ICS valve fitted to the hot gas line is designed to prevent too low discharge pressure at the compressors.
    the liquid to oil coolers must be connected at the bottom of liquid receiver and the liquid line to LP vessels higher.
    fans controlers have to be downstream of the check valve.

    regards
    I have couple concerns about this drawing. Probably, check valve should have opposite direction. Pressure in TSR will be very low and it will be not enough to move liquid to LPR or IPR.

  19. #19
    Join Date
    Nov 2009
    Location
    france
    Age
    64
    Posts
    225
    Rep Power
    19

    Re: Condensing pressure regulator with thermosyphon oil cooling

    Sorry Segei
    old guy, old school, wrong symbol but gas flow still from compressor to condenser. The topic was hot gas defrost and thermosyphon oil cooling, so this is to prevent the draining of the liquid receiver to the hot gas line during defrost and oil or discharge temperature trip-out of the compressor. In any case, the condenser capacity should be adapted to the air temperature, at least, valving of one condenser is necessary.

  20. #20
    Join Date
    Mar 2013
    Location
    Korea
    Posts
    10
    Rep Power
    0

    Re: Condensing pressure regulator with thermosyphon oil cooling

    Thank you cricri,
    but apart from the check valve the ICS 1 for Hot Gas have to control pressure not before but after itself to manage about 6 - 7 bars inside evaporators defrosting pressure (CVC pilot). ICS2 is CVP (HP) (set 8 - 9 bars).

  21. #21
    Join Date
    Nov 2009
    Location
    france
    Age
    64
    Posts
    225
    Rep Power
    19

    Re: Condensing pressure regulator with thermosyphon oil cooling

    Hi Andrew,
    ICS1 is not absolutely necessary, the control is upstream. It's to prevent a too low discharge pressure causing oil carryover and a noisy compressor.

  22. #22
    Join Date
    Mar 2013
    Location
    Korea
    Posts
    10
    Rep Power
    0

    Re: Condensing pressure regulator with thermosyphon oil cooling

    Hi, Cricri,
    I think ICS1 + CVC we need to protect LP evaporators, plate freezers of excessive high pressure (can be as example in summer). But check valve may be not absolutely necessary.
    Regards

  23. #23
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Condensing pressure regulator with thermosyphon oil cooling

    Quote Originally Posted by Andrew5447 View Post
    Thanks, Ranger 1, I think you are right. If we stop equalizing line, the high pressure receiver will be on pressure that is higher then in condensers lines and the pilot receiver, they will be overfilled by liquid. The working area of flooded condenser go down and at some I see liquid can drain to high pressure receiver. I hope it will be without hammering.
    The question is how to combine condensing pressure regulator and thermosyphon oil cooling.
    Amot valve or similar for t/syphon oil cooler, as I think you should have this regardless in your climate. Amot type basically controls oil temp by bypassing or mixing oil around oil cooler to maintain set temp (50 deg C).

  24. #24
    Join Date
    Dec 2012
    Location
    Canada
    Age
    58
    Posts
    7
    Rep Power
    0

    Re: Condensing pressure regulator with thermosyphon oil cooling

    May I suggest that your problems and solutions are with your Hot Gas Defrost system. I have seen this exact problem before and all we did was install a pressure regulator for the Hot Gas System and increasing the length of the defrosts and/or their frequency as required. We ended up running the Hot Gas System around 80 to 90 psi and the funny thing was that because our pressure was always constant throughout the year, no more small ammonia leaks at the evaporators...
    In my opinion, the overall hot gas system is one of the most overlooked pieces of a well functioning system. You will have to spend sometime experimenting with the individual evaporators to see what does work best. I have found that more frequent defrosts with shorter durations works best...
    Kherson

  25. #25
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Condensing pressure regulator with thermosyphon oil cooling

    It is not energy efficient to increase frequency of defrost. 80- 90 psig is it pressure in hot gas line or pressure in the evaporators?

  26. #26
    Join Date
    Mar 2013
    Location
    Korea
    Posts
    10
    Rep Power
    0

    Re: Condensing pressure regulator with thermosyphon oil cooling

    Thank you All!
    Now I install only one ICS with CVP(HP) and EVM (wide open for summer) before condenser on discharge line and I use classical Thermosyphone oil cooling.
    And I use ICS for Hot Gas Defrost Line to control pressure not before but after itself to manage about 6 bars inside evaporators defrosting pressure (CVC pilot).
    Cold winter put everything in its place.