Results 1 to 10 of 10
    Apr 2012
    Iraq
    29
    610
    10
    electric devices
    what are the utility of those devices
    1 which connected the high speed of outdoor fan speed L supply
    2 same type connect the contactor and L of indoor unit
    the system type is as below
    samsung uqt24s6gea
    hookster's Avatar
    hookster is offline Veteran Poster I am starting to push the Mods: of RE
    Apr 2007
    Hampshire
    431
    Re: electric devices
    They look like RC filters (low Pass), this is to prevent harmonics from the inverters.
    69
    10,477
    Sometimes used across the contactor coil circuit to prevent 'spikes' in the electrics when the coil is switched on/off.
    http://uk.rs-online.com/web/p/contac...ories/0759128/
    Somerset
    63
    4,518
    38
    As Brian Say's, the problem is not so much when the contactor is de-energised, But when the contactor is disconnecting.
    I am led to believe that whilst the contacts are separating there can be a huge "in-rush of current across the contacts.
    These help smooth the current and therefore protect and prolong the actual contacts from damage.
    Apr 2012
    Iraq
    29
    610
    10
    thank all
    you said it will prevent the sparks in the contactor
    so what about the first question
    http://www.refrigeration-engineer.co...153913&thumb=1
    Jun 2012
    Austria
    42
    15
    It's the same question, isn't it? Prevents sparks so protecting equipment from damage (also prevents interference).
    Apr 2012
    Iraq
    29
    610
    10
    thank u all
    Jul 2013
    55
    5
    They certainly look like snubber caps. I'm surprised there's no series resistor to prevent current spikes when the contactor closes, but maybe they're special ones with that resistor integrated.
    Here's a snubber in one of my designs:
    You can clearly see the resistor in series with the snubber capacitor. (That pink package is a surge protector.)
    Jul 2013
    US
    Quote Originally Posted by kefah View Post
    samsung uqt24s6gea
    You can see from the markings on these that they are indeed RC snubbers. They are generally used across the contactor coil to prevent inductive flyback (spikes) to upstream electronics when the coil de-energizes. I use them on all contactors to prevent damage to my PLC's.
    From your description I would say these snubbers are to prevent inductive flyback from the motor that causes burned contacts - same effect, different location.
    Inductive spike only occurs when the coil de-energizes. (The fan motor is essentially a big coil.) The spark you see when the contacts close is actually caused by contact bounce.
    Apr 2012
    Iraq
    29
    610
    10
    ok
    thank u all
