    Show us your installs....



    Thought I would kick this off with a couple of photo's of a recent Ground Source Heat Pump rebuild. Original system failed due to a split BPHE causing the ground loop to mix with the fridge side. Had to provide a replacement compressor, BPHE's, safeties and pipework. Kept the same controller.







  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Show us your installs....

    Here's a picture of the original layout


  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Show us your installs....

    nice job, but u insulated the liq line!
    feel free to remove this comment if you like

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Show us your installs....

    Quote Originally Posted by install monkey View Post
    nice job, but u insulated the liq line!
    feel free to remove this comment if you like
    Bu**er....could have saved some money

  5. #5
    Join Date
    Jul 2009
    Location
    South Africa
    Age
    78
    Posts
    195
    Rep Power
    17

    Re: Show us your installs....

    Wow, that looks a lot neater than my fridge units. Can I ask how did you get the tube type foam insulation on the pipework after it was welded?

  6. #6
    Join Date
    Dec 2007
    Location
    ireland
    Age
    54
    Posts
    275
    Rep Power
    26

    Re: Show us your installs....

    Why add the oil seperator, accumalator and bypass valve? or are there parts hidden from view on the original

  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Show us your installs....

    On the original setup, we found that one of the PHE's was filled with oil when we disassembled it, thinking that it was short cycling, thus not allowing time for the oil to be returned to the comp, so we built in the oil separator to prevent oil carryover.

    As the unit is reversible, we were concerned that, on change over (it doesn't off cycle to do it) the compressor could be susceptible to liquid flood back without the accumulator. Also, as it changes mode, the time required by the hot gas to push the liquid out of the PHE caused the LP switch to trip, thereby stopping the unit.

    I have built in the HGB valve on a double pole delay timer which bypasses the LP and HGB's for 40 secs, which now allows change over without tripping/stopping.

  8. #8
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Show us your installs....

    Quote Originally Posted by Frikkie View Post
    Wow, that looks a lot neater than my fridge units. Can I ask how did you get the tube type foam insulation on the pipework after it was welded?
    You cut the insulation tube with scissors or stanley knife and then use glue on the seams.

  9. #9
    Join Date
    Jul 2009
    Location
    South Africa
    Age
    78
    Posts
    195
    Rep Power
    17

    Re: Show us your installs....

    Quote Originally Posted by frank View Post
    You cut the insulation tube with scissors or stanley knife and then use glue on the seams.
    Thanks for the info, I've also tried cutting and gluing the insulation but it never looks as neat as yours

  10. #10
    Join Date
    Dec 2007
    Location
    ireland
    Age
    54
    Posts
    275
    Rep Power
    26

    Re: Show us your installs....

    Ok makes sense, perhaps a case of how it was made and how it should have been made.Manufacturers tend to lose a lot of parts to make their costs cheaper

  11. #11
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Show us your installs....

    Quote Originally Posted by joe-ice View Post
    Ok makes sense, perhaps a case of how it was made and how it should have been made.Manufacturers tend to lose a lot of parts to make their costs cheaper
    Spot on Joe.

    Don't want the customer chasing me if the unit failed a second time because of poor design.

  12. #12
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Show us your installs....

    HI.
    If you are lucky you have a slitting knife, which makes the job even easier.
    Ones like the attached are quite cheap here in the UK at least (around £10.00)
    Grizzly

  13. #13
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

  14. #14
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Show us your installs....

    Nice work Frank!

    Was aiming for an old school look with this one...

    https://www.youtube.com/watch?v=pSBr5qB5OPk

    Ice builder system,

    https://www.youtube.com/watch?v=cFX9aRR2Dlc

    Two more cheese stores....

    https://www.youtube.com/watch?v=U0GjSzIPtgM

    Mostly found in Oxfordshire, UK :)

  15. #15
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Show us your installs....

    Mostly found in Oxfordshire, UK :)

  16. #16
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: Show us your installs....

    Quote Originally Posted by Grizzly View Post
    HI.
    If you are lucky you have a slitting knife, which makes the job even easier.
    Ones like the attached are quite cheap here in the UK at least (around £10.00)
    Grizzly
    I haven't see those knives here so i ordered one from Ryanairspares. Thanks Grizzly