Results 1 to 15 of 15
  1. #1
    Join Date
    Oct 2012
    Location
    BRAZIL
    Age
    33
    Posts
    5
    Rep Power
    0

    ammonia and humidity



    Hi guys,
    I want to know what problems can i have if my instalation have alot of water in the amonia system.
    Than you all



  2. #2
    Join Date
    Feb 2013
    Location
    Rochester, NY
    Posts
    37
    Rep Power
    0

    Re: ammonia and humidity

    Hi,

    If your charge is starting to get aqueous you'll find you need to pull lower suction pressures to get the same refrigeration effect. There is also the chance of freezing up expansion valves.
    Last edited by Iceman717; 20-03-2013 at 02:43 PM.
    Iceman717

    ---
    Compressors in the basement, condensers on the roof, evaporators everywhere else. :cool:

  3. #3
    Join Date
    Jul 2006
    Location
    USA
    Age
    73
    Posts
    865
    Rep Power
    26

    Re: ammonia and humidity

    It depends on what you mean by a lot of water.
    I once had a oil cooler splt on a medium temp installation with Vilter compressors. We had enough water in it that we had to do repeated oil changes on five compressors.
    We never went down but kept draining oil from the vessels until we got out as much as we could.
    That being said it is never a good thing, but it is not uncommon to have some water in an NH3 system. It is almost impossible to avoid over time if you run into a vacuum.
    Equipment is avaiable to remove water if you wish to install it.
    If you have a two stage system the water tends to collect in the intercooler where you can easily drain it.
    You can remove a great of water (not all) over time if you have a oil pot that you can valve off and pump out.

  4. #4
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,035
    Blog Entries
    4
    Rep Power
    31

    Re: ammonia and humidity

    regulating valve freezes over, acid in compressor oil, etc etc
    -Cheers-

    Tycho

  5. #5
    Join Date
    Sep 2006
    Location
    Venezuela
    Posts
    259
    Rep Power
    18

    Re: ammonia and humidity

    In a soft drink instillation working at Te=-2ēC ,Flooded cooler. I found the the oil + ammonia + water form a kind of paste that damaged the compressor (Vilter Recip).
    Normally a very low percentage of water is good to avoid corrosion in the carbon steal but to much is very dangerus and you loose eficiency
    chears
    Gwapa

  6. #6
    Join Date
    Dec 2008
    Location
    chapeco
    Age
    39
    Posts
    62
    Rep Power
    16

    Re: ammonia and humidity

    The contamination of water can occur in a facility since the period of
    installation and assembly even during normal operation of the system.
    Contamination during assembly:
    • Condensation (moisture) inside the pipe during unprotected
    assembly;
    • Equipment, piping and other components exposed to the weather during
    the assembly period without protection or without internal pressurization (with
    Nitrogen, for example);
    • Pressure vessels after hydrostatic testing cos that were poorly drained;
    • Condensation (moisture) due to test co pneumatic air lines uti lizando
    moist;
    • Vacuum poorly done (or not done);
    • Initial charge Ammonia the presence of water (from suppliers not
    qualifi ed). Should be required certi fi cate of the purity (99.95%) Load of Ammonia
    being supplied.
    Contamination during the operation:
    • Break-tube exchangers "Shell-and-Tube", mainly in coolers
    water or condenser water;
    • Procedures not suitable oil drain or vent Ammonia
    Potted during maintenance or rows, with pressure below atmospheric
    (Tev <-33.5oC). The risk increases when the purging is done for water tanks
    and in this case it is recommended to install check valves on the line
    purge to prevent the counter-fl ow water to penetrate inside the circuit
    cooling;
    24
    Small leaks in valves, • gaskets, seals for pumps, compressor seals
    and serpenti the evaporator when operating at low pressures (with
    Tev <-33.5oC), or even gathering operation;
    • Procedure vacuum unsuitable after maintenance of equipment
    system. Often it is not done the vacuum;
    • Ammonia uti Lizada for replacement with presence of water (from
    suppliers unskilled markets).
    However, it is not always possible to prevent water penetration into the system. Beyond
    care with drainage and with the vacuum fi ca dif ficult to evaluate the contamination along
    the years but the analysis of samples at various points in the installation.
    One way to observe how much water penetrates into systems with low
    pressures which have air vents is by monitoring the air vent. It
    Importantly, the air that eventually enters the refrigerant circuit
    Have moisture, but the air is vented which is completely dry since water is solubilizes
    with Ammonia and fi ca accumulated in the system. When considering a period of 10 years
    is not surprising to find 5-10% of water in the system.
    A survey in the 90 [3] in more than 100 facilities in Denmark,
    Norway and Sweden, has shown that most of them continue containing about 2% to 6% water
    and more than 10% of the plants had more than 8% of water on
    liquid separator at low pressure side.

  7. #7
    Join Date
    Feb 2010
    Location
    new zealand
    Age
    42
    Posts
    67
    Rep Power
    15

    Re: ammonia and humidity

    As with NH3LVR, there is water then there is water! IMG_0353.jpg
    believe it or not that is an Ammonia sample, from a system that took on almost 60% of the charge in sea water the damage was horrendous and cost millions. the system is now back and running 2 years on and hasnt skipped a beat since the last oil change 1000 hrs ago.

  8. #8
    Join Date
    Apr 2008
    Location
    Canada
    Posts
    253
    Blog Entries
    4
    Rep Power
    20

    Re: ammonia and humidity

    60%!!! How did so much water get in the system?

  9. #9
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: ammonia and humidity

    Hi, gui.furlan

    Quote Originally Posted by gui.furlan View Post
    Hi guys,
    I want to know what problems can i have if my instalation have alot of water in the amonia system.
    Than you all
    Like said above you can have a lot of problems, but it is better to read all about by yourself

    what you need ...refrigeration grade ammonia ...
    http://www.tannerind.com/anh-specifications.html


    ammonia properties ....
    https://www.osha.gov/SLTC/etools/amm...ation/ammonia/


    about contaminated refrigerant ... ammonia in this case ...
    http://www.airgasspecialtyproducts.c...igeration.aspx

    Hope this will give you some useful information ...

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  10. #10
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: ammonia and humidity

    If it is sea water that contaminated the system, I would guess a water cooled condenser?

    The rest is pure physics.
    Grizzly.

  11. #11
    Join Date
    Feb 2010
    Location
    new zealand
    Age
    42
    Posts
    67
    Rep Power
    15

    Re: ammonia and humidity

    It was caused by a Static coil fracture on a Tuna well, the chief engineer took off as soon as the boat docked all three compressors died less than a week later.

  12. #12
    Join Date
    Nov 2013
    Location
    Mauritius
    Age
    46
    Posts
    2
    Rep Power
    0

    Re: ammonia and humidity

    Hi Josip,

    I have seen the link that you provided for the quality of ammonia and would like to thank you for sharing this information.

    However I am facing an issue these days with one screw compressor. The system was running fine until the previous week-end where we purged oil from the evaporator and added some ammonia. since then the system is behaving very bad and is creating havoc. We are having High suction pressure on the compressor (screw) and the oil is also getting the tendency to get carried over.

    I am strongly believing that the ammonia is not the right quality but until now the supplier is claiming that the batch is OK and he is even arranging COA for me.

    I would like to know :
    1. Is there a standard for the cylinders of Ammonia Anhydrous refrigeration grade, in terms of colour/Size etc?
    2. When I recieve the cylinders on what test can be done to know that it is really the grade for R717? We are trying to do a Pressure/Temperature Mesurement on the cylinder, but is there a kit or another means to measure this purity/water content?
    3. If I got it right, if there is high moisture content in the ammonia, the oil would have a tendency to get Acidic. Am I right in this statement? Testing the acidity of the oil, as compared to another compressor which has not had this new batch of ammonia could give me an indication of the moisture content of this new ammonia batch?

    Basically I want to rule out the ammonia quality first before I open the compressor.

    If anyone has some information, grateful if you could share it.

    Thanks,
    Vish

  13. #13
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: ammonia and humidity

    Hi, Vish

    welcome to RE forums ....


    Quote Originally Posted by Vish View Post
    Hi Josip,

    I have seen the link that you provided for the quality of ammonia and would like to thank you for sharing this information.

    However I am facing an issue these days with one screw compressor. The system was running fine until the previous week-end where we purged oil from the evaporator and added some ammonia. since then the system is behaving very bad and is creating havoc. We are having High suction pressure on the compressor (screw) and the oil is also getting the tendency to get carried over.

    I am strongly believing that the ammonia is not the right quality but until now the supplier is claiming that the batch is OK and he is even arranging COA for me.

    I would like to know :
    1. Is there a standard for the cylinders of Ammonia Anhydrous refrigeration grade, in terms of colour/Size etc?
    yes there are some standards, not unified ... but the best is to check by yourself ....

    http://www.psych.usyd.edu.au/whs/COP...der_Safety.pdf
    http://gkrss.ru/services_en/fillingthecylinders.html
    http://www.transcaer.com/docs/AATour...dout_rev04.pdf
    http://www.tannerind.com/PDF/blue-anhy-amm.pdf


    Quote Originally Posted by Vish View Post
    2. When I recieve the cylinders on what test can be done to know that it is really the grade for R717? We are trying to do a Pressure/Temperature Mesurement on the cylinder, but is there a kit or another means to measure this purity/water content?
    ... not sure about kit, but there are small (1 or 2 lit cylinder) to take a sample and send it to lab ... not sure what is available in your country ....

    Pressure/Temp mesurement ... the best is to put your cylinder with ammonia into cold room with known temperature and then the very next day you can check the pressure ... but you need precise thermometer and gauge ... it is simple but will not tell you too much ...


    Quote Originally Posted by Vish View Post
    3. If I got it right, if there is high moisture content in the ammonia, the oil would have a tendency to get Acidic. Am I right in this statement? Testing the acidity of the oil, as compared to another compressor which has not had this new batch of ammonia could give me an indication of the moisture content of this new ammonia batch?

    Basically I want to rule out the ammonia quality first before I open the compressor.

    If anyone has some information, grateful if you could share it.

    Thanks,
    Vish
    there are available kits to check oil .... but again you need to send a sample to lab .... like this one ....
    https://www.refparts.york.com/ALLPar...OilChoice.aspx


    Not sure what kind is your plant, but it is possible to install air purger and water purger unit to avoid future problems ...

    http://www.hantech.com/products/pages/ap.htm
    http://www.hantech.com/library/pdfs/...AmmoniaSys.pdf
    http://www.hantech.com/documents/PDF/APP001.pdf


    also you can search RE archive to find some more info all about refrigeration and other things
    ... http://www.refrigeration-engineer.co...hive/index.php


    Hope this is of some help to you.


    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  14. #14
    Join Date
    Nov 2013
    Location
    Mauritius
    Age
    46
    Posts
    2
    Rep Power
    0

    Re: ammonia and humidity

    Thanks Josip,

    Will go throught the information that you provided and get back to you if in need.

    Regs,

  15. #15
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: ammonia and humidity

    Quote Originally Posted by Vish View Post
    Hi Josip,

    I have seen the link that you provided for the quality of ammonia and would like to thank you for sharing this information.

    However I am facing an issue these days with one screw compressor. The system was running fine until the previous week-end where we purged oil from the evaporator and added some ammonia. since then the system is behaving very bad and is creating havoc. We are having High suction pressure on the compressor (screw) and the oil is also getting the tendency to get carried over.


    I am strongly believing that the ammonia is not the right quality but until now the supplier is claiming that the batch is OK and he is even arranging COA for me.

    I would like to know :
    1. Is there a standard for the cylinders of Ammonia Anhydrous refrigeration grade, in terms of colour/Size etc?
    2. When I recieve the cylinders on what test can be done to know that it is really the grade for R717? We are trying to do a Pressure/Temperature Mesurement on the cylinder, but is there a kit or another means to measure this purity/water content?
    3. If I got it right, if there is high moisture content in the ammonia, the oil would have a tendency to get Acidic. Am I right in this statement? Testing the acidity of the oil, as compared to another compressor which has not had this new batch of ammonia could give me an indication of the moisture content of this new ammonia batch?

    Basically I want to rule out the ammonia quality first before I open the compressor.

    If anyone has some information, grateful if you could share it.

    Thanks,
    Vish


    Vish, can you clarify if this screw compressor in question has a high suction or discharge pressure.
    If its high suction pressure, is machine fully loaded would be the obvious thing to check first.

    If you can detail what is doing pressures etc as just adding ammonia even with water in it cannot be the only possible problem.

    How much did you add & where did you add it?

    Sometimes a lot of things happen by coincidence & it can throw you off.

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •